Hi all. I'm planning to connect 2 x 5kw quattros in parallel as I need both 120v and 240v.
I have a 6kw 240v generator. Can I connect it to both inverters? I would really appreciate any guidance or a wiring diagram example
Thanks
Hi all. I'm planning to connect 2 x 5kw quattros in parallel as I need both 120v and 240v.
I have a 6kw 240v generator. Can I connect it to both inverters? I would really appreciate any guidance or a wiring diagram example
Thanks
L1, N, G to L1 Quattro
L2, N, G to L2 Quattro
Man I can't thank you enough. The diagram is brilliant.
A small question, do I need a MK3-USB cable to configure a split phase for quattros? Or can I connect the two quattros and then one to my cerbo GX and then configure split phase using the app? Will I be able to update quattros firmware without mk3-usb cable?
Thanks again!
Unfortunately, the only way I know to do it is with VE.Bus and VE.Config on PC via MK3-USB.
Try this:
Appears you need a MK3-USB or smart-dongle.
Thanks again for all your info.
I found also this discussion, where someone says you could use VRM portal to modify the inverter settings:
https://diysolarforum.com/threads/accessing-victron-multiplus-settings.27611/
That would be awesome if it works, will give it a try.
Yes, you can change the configuration of ONE inverter via that method. I do it regularly; however, that requires a GX device for VRM operation, and VEConfigure doesn't configure inverters for parallel operations - only single inverter settings.
You are going to need a MK3-USB with VEBus/VEConfig or a smart dongle and Victron Connect to configure them in parallel.
Is your system already in parallel?
Thanks @snoobler , no I haven't configured it yet. I have everything ready to disconnect my old inverter and connect 2 new quattros. In the victron app I found a demo mode where you can actually simulate viewing/changing device settings and I didn't see the split phase configuration there. Is it what you meant? I can modify a single inverter settings but for advanced stuff (like a split phase configuration) I need a mk3-usb cable
And also wanted to ask. I will be wiring inverters to my AC breaker panel. Do I need breakers between the inverters and the AC panel? If yes what kind of breaker would I need? I assume 5kw quattros with a theoretical 10kw peak, 80amp breaker?
Thanks again so much for all your help
Yep. You'll definitely need a MK3-USB
Recommend you create an account here:
https://professional.victronenergy.com/
Watch the Online Training: 9.2 - Three-phase & Parallel installation
Yes. You will need a dual pole breaker to break L1 and L2. I have one of these between my Quattro output and AC panel:
and this 50A breaker:
https://www.homedepot.com/p/Eaton-BR-50-Amp-2-Pole-Circuit-Breaker-BR250/100125397
While it's listed as a 5kW unit, it's really a 4kW unit with a 30 minute 5kW limit, so I sized for 4000W each. 8000W/250V = 33.3A. 1.25 * 33.3 = 41.7A, so I sized up to 50A. The 6-3 Romex is rated for 55A, so I'm good.