question

john2019 avatar image
john2019 asked

Modbus Reading mutiplus

Hi, All

I use a MK3 cable to connect with mutiplus. I downloaded two softwares ModScan and Modbus poll and try to read 04 input register. I set slave unit ID is 246 (from CCGX) address is from 15 to 20 (not sure correct) length is 6... baud rate 9600 , word length 8 , no parity and close bit 1....... But can not get response from mutiplus. Any suggestion for software and settings to read infor from mutiplus or CCgx. Many thanks

Modbus TCP
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Ole Saether avatar image
Ole Saether answered ·

As far as I know, the Multuplus does not support Modbus over the MK3 dongle. You need to connect the Multiplus to the CCGX with a VE.Bus cable and then you can access it over ModbusTCP via the CCGX. See the CCGX manual on how to connect them together:
https://www.victronenergy.com/live/ccgx:start

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources