bonjour,

Qui pourrait me confirmer que le câble est bon? SVP.........couplage AC OFF GRID.

sans fusible sur le neutre ou avec? (notice du ET112)couplageac-solis.pngcouplageac-solis.pngcouplageac-solis.png(143.1 KiB)

et112 pv readings
couplageac-solis.png (143.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
sharpener avatar image
sharpener answered ·

I have exactly the same arrangement with 4kW of Steca inverters. Works fine.

No fuse for the ET112 as I consider the 20A circuit breaker is small enough to provide reasonable protection in the case of an internal fault.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

yvond avatar image
yvond answered ·

bonjour et merci de votre réponse.

donc, pas besoin de mettre un autre disjoncteur de protection entre le Solis et le ET112?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sharpener avatar image
sharpener answered ·

No. I have not got one and I have not seen them in any published schematics. I do not think any additional protection is necessary here.

Also you asked about the RJ45 sockets on the ET112. If I remember correctly these are simply an alternative to the screw terminal connections, they are not a network connection.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

yvond avatar image
yvond answered ·

bonjour et merci pour les réponses Sharpener.

Je vais donc câbler comme sur le schémas.

bonne journée.