Cell balancing 48v battery bank, 2 out of 6 batteries status unknown


Hello,

I charged the 200ah 24v individually before connecting them in series and as you can see in below picture two batteries balance well but does not change status from unknown to balanced as the other four does. In the standard ess settings absorption time is 1hr but I have read that 2hrs is recommended. I can change it, no problem to hopefully give time for proper balancing but..

1. Why is the standard ess setting 1hr while recommendation is 2hrs?

2. Why does the four out of six batteries reach status balanced given the same starting conditions?


/Daniel



img-1287.pngimg-1288.png




Battery Balanceress settings
img-1287.png (159.4 KiB)
img-1288.png (268.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
klim8skeptic avatar image
klim8skeptic answered ·

@Cronblad If you click on the "info" button Victron Connect will give an explanation of what "Unknown" means, and what is required to remedy the situation.

vc-batt-status.png

As per the Smart Lithium Battery manual. The cell balancing process is nearing completion when all cells have reached a voltage of 3.55V and the charge current has dropped below 1.5A. Balancing is complete when the charge current has dropped even further.


vc-batt-status.png (325.7 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cronblad avatar image cronblad commented ·

Thank you! According to definition of "Unknown" any cell imbalance shall be detected when battery is above 13,8v x 4= 55,2v. My max charge voltage is set to 56,8v per the manual so this one should be ok.


Regarding the note:

First prerequisite: "The cell balancing process is nearing completion when all cells have reached a voltage of 3.55V and the charge current has dropped below 1.5A. Balancing is complete when the charge current has dropped even further" 3,55v per cell = 3,55v x 16 cells in my case (48v system)= 56,8v This prerequisite is fulfilled.

Second prerequisite: The only thing I can think of right now that keep the batteries from reaching "balanced" status is that 1hr absorption time is not enough for the charge current to drop below 1,5A. Hope someone can explain my question no.1 above why 1hr is set as standard in the ESS if it´s not enough.

And also, why has 4 out of 6 batteries reached status "balanced" and not the last 2?



0 Likes 0 ·
klim8skeptic avatar image
klim8skeptic answered ·

@Cronblad And also, why has 4 out of 6 batteries reached status "balanced" and not the last 2?

As per the manual, "unknown" means the battery has not been fully charged and fully balanced in the last 30 days.

Solution? Charge the batteries as per manual until their status goes to "balanced".

To keep the batteries happy and balanced you need to ensure that they spend enough time in "absorption" every month, as outlined in the manual.

As per why ESS only has 1 hour absorp time, dunno. Perhaps they expect the batteries to be fully charged every couple of days??


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cronblad avatar image cronblad commented ·

Thank you! Appreciate it!

1 Like 1 ·
cronblad avatar image
cronblad answered ·

Edit: Problem eventually sorted by disconnecting the batteries that did not balance and charged them stand alone over and over a few times.