I want to add two emergency-stop switches to my Multi RS 6000 with two 16 kWh batteries.
Which version should I choose? How many NO and NC contacts?
At Eletrobode, I have a choice, especially since I also want to order two changeover switches here, but the prices vary considerably between the different versions.
I think the emergency stop should be incorporated into the jumper wire of the RS 6000?
Hi, I’ve also built an emergency stop system myself, with 2 emergency stop buttons (in 2 locations), each with 3 NC contacts.
The NC contacts are connected to the remote input of each of my 3 MultiPlus units, and I use the 12 V output from one of the MultiPlus units to de-energise a relay to which my 4 Pylontech batteries have a remote contact for switching them off.
Switching on is done with a reset button that switches on the batteries, followed by the MultiPlus units.
This is fail-safe and leaves the system de-energised in an emergency, switching off both the MultiPlus units and the batteries.
At the moment, there are still no official regulations for home batteries; there is only advice to comply with the PGS37 standards. Regulations are on the way, though.
No, not a momentary push button; this is only when using an emergency-stop assistant.
There is currently a wire link in the remote connection. If you pull it out, the system switches off, so with a MultiPlus it needs to be an NC contact that remains off.
This is one of the emergency stops:
Pressing it switches the system off, and turning it switches it back on.
Implementing an emergency stop that switches off the AC side is easy to achieve with Victron, but how could you disconnect the DC side from the inverter and, preferably, disconnect the battery packs from each other as well? In other words, disconnect each pack individually from the DC busbar. That way, one pack cannot continue supplying power to another in an emergency.
The only solution I can think of is to install a TBS battery relay between the battery pack and the DC busbar, and have it switched off via the Cerbo and/or an emergency signal.
This is also with a view to future guidelines for larger battery banks.
I’m curious whether anyone has already implemented this?
Toby (Helion Energie) has provided an example based on a Victron Lynx Smart BMS. What I see as a shortcoming of that solution is that it disconnects the batteries from the DC busbar as a whole, but not individually. In a worst-case scenario where one pack overheats due to an internal fault, the other battery packs could still supply energy to the faulty pack, even though the DC busbar is disconnected by the Smart BMS.
It may be a bit far-fetched, but if we’re going to think through emergency scenarios, we might as well go all the way
Either a hand operated Victron DC switch or a good 60 volt 200A DC relais on every battery, avoid those cheaply ‘dc car switches’ many can’t handle 56 volt and their contact resistance is high…= heat = danger.
The bms of Pylontech batteries can switch off the DC output by a remote contact, example 2 contacts in a emergency switch, one for the inverter and 1 for the pylontech (or 3+1 contacts in a 3 phase Victron ess)
I have indeed seen discussions more often about the quality of DC switches. The only relay I’ve been able to find for this purpose is TBS’s battery relay.
I’ve now looked at battery packs from various manufacturers, and I haven’t come across an emergency-stop input on any of them yet. I’ll have a look at Pylontech. Not all packs are fitted with a circuit breaker either.