I don’t think so, i assumed the mppt will adjust voltage until current is below 12A regardless of what wattage the tracker is handling.

Back a couple years ago I didn’t have a lot of spare scc capacity so I connected two 10S series strings in parallel to each of my rs450/100 trackers. 375W panels, 41.1 Voc, 11.65 Isc, 34.9 Vmp, 10.75A Imp. So massive overpanelling of nearly 3x, nearly 15kW of panels, theoretically over 23A…per tracker

But in practice, the 4kW per tracker limit kicks in much sooner, at 349V operational string voltage the tracker only needs 11.4A to deliver the max 4kW. And with the 450/100 theres an overall output limit of 100A as well so its basically two 450/50s from a planning perspective. Now maybe it becomes a problem with larger 600W+ panel sizing?

Where im installing people generally have very little space so indeed, small strings. Think 4 panels sometimes. I know an mppt 250 could do that but that’s another component to install + more expensive, or i could use the easysolar, i know, lots of options with victron.

The point i’m trying to make is the multi rs solar would be more usefull to me with 16A inputs like most inverters. My goto solution is to install sma instead of victron.

And in case you want to mention that NOCT is fine:

In spring and autumn in particular, you can get close to 15A. The other day, I saw 15.7A on my Aiko 490s on the RS MPPT 450. The modules would then be limited by the 12A.

Try explaining that to a customer.

Nothing to do with “properly designed” – most of the new high-efficiency panels on the market need a ~15A rated MPPT to be able to use the full capacity of the panel (up to 500W now for 54 cell panels, the most common size by far).

Losing 20% of maximum output with a 12A-rated Multi RS Solar is equivalent to turning a 500W panel into a 400W one, or a 25% efficient panel into a 20% efficient one – in full sunlight, of course.

Meaning you’ve either wasted 20% of your money, or 20% of your roof area… :frowning:

Ah, yes. For me with my 250/100 and 250/85s they are perfect for 4s or 5s strings, three of four in parallel at different orientations and steady output throughout the day.

But for how many panels in series?

Because with 450v mppts, you need to aim around 300v per string to be the most efficient.

Inverters with 450-600v mppts are not meant for short strings but for long ones.

If you use 4 or 5 aiko panels yes you will be around 200v, so you will be limited by the 12A impp, but if you use more, lets say 8 panels, then you will be higher than 250v and the 12A impp will not be what is limiting your panels. In this case what will limit the panels is the max 3000w output per tracker.

We currently have the JAM54D41-460 in stock. If you’re talking about very short strings, in this case you mean strings with fewer than 8 modules (because Vmp 33.68 V * 8 = 269.44 V > 250 V). If you’re talking about 30% oversizing, you mean strings with 8 (22%) or 9 (38%) modules.

Looking at the curves in the characteristic graph, I actually agree with you that this usually works. So perhaps it’s a solution for my own home project, where I spend months weighing up what would probably be the best option.

But when I plan several projects every week, it doesn’t make sense to fit every roof with arrays containing an exact multiple of 8 or 9 panels.
And on average, one person in ten will still look at the datasheet and say, that’s more than 3 kW, so it’ll be curtailed. The discussion takes time, so why put myself through that?

(EDIT: I’ve attached the datasheet for you as well :wink: )

JA Solar JAM54D41 LR Datenblatt.pdf (680,4 KB)

I’ve seen a few people comment its OK and under the current limit if you use a higher voltage string and max power ratings are being throttled. To be clear, the units have a max voltage range, a max current input and a max power input per tracker. You are meant to design within these specs and not hope something happens to throttle the output on your behalf because you couldn’t source the right panels.
As others have said, its its not running efficiently (MPP) you’ve overspent or wasted roof space with mediocre performance.

It doesn’t matter which limitation I run up against.

A customer won’t understand it when there are high-performance modules on the roof.

At least with those (Impp=13.7A) you’re only giving up 12% of the maximum available power using a 12A Multi RS Solar, as opposed to up to 20% for (widely available) higher output panels – either way, it turns all similar 54-cell panels into ~400W ones, like those from 5 years ago… :frowning:

I can’t see anything good about 12%.

A product (new to the market) has specs that don’t fit the market conditions.

Or is it not intended for rooftop installations that aren’t optimally oriented, with high-performance modules, @M_Lange?

Now I remember why the Multi RS was ruled out for me, too. It only has 12A.

Yes, it’s really very hard to understand that a 3kW inverter can only produce 3kW of power. Practically impossible to explain.

Perhaps because specific requirements are more likely to lead you to Victron, and the others can’t do those things after all.

Let’s take 6 AIKO A490 MCE54Dw panels in a string.

That gives you 6x0.49=2.94 kWp

With Uoc=41.1V

Ump=34.7V

Isc=14.88A

Imp=14.13A

Pmodule less than 3kW. How much does the RS19 take at maximum? That’s exactly what this is about.

Exactly, this is about limiting the current, not the total power. I thought you hadn’t understood that, given your comment: “It doesn’t matter at all which limit I run into.”

Another perspective: In many cases (number of modules, location, orientation), the loss due to current limiting, relative to the annual yield, will be well below 1%, often close to 0%. And the loss only occurs when a lot of PV electricity is being generated anyway.

A feed-in limit hardwired into the hardware, so to speak.

The control unit will arrive at some point. Then I’ll be allowed and able to feed 100% into the grid.

You’re allowed to, but you can’t.

Never mind the fact that my peak self-consumption also gets close to 100% in summer.

Those 6 490W Aiko panels (same as I’ve now got) are capable of producing 2.94kW (at 1kW/m2 solar irradiance), but when connected to a Multi RS Solar this will be restricted to 2.50kW by the 12A current limit, which is 15% lower. So you’ve paid for nice new advanced 490W (Pmax) panels, but are only really getting 416W (Pmax) panels. Not an issue when solar irradiance is below 850W/m2, but still annoying – and unnecessary.

When you sell a design do you explain the difference between STC rating and the far more common day to day NOCT for example? There must be some client education or they’ll actually be expecting nameplate values?

The modules mentioned are currently running at Impp 15.1…15.6 A on my RS MPPT 450/200, well above NOCT and STC, because the weather is cool.