Using a Weize 1210012V Deep cycle GEL battery with 75/15 and 2 100W panels wired in parallel.
Cycle Use: 14.1-14.1
Standby Use: 13.5-13.8
What should the setting be on the charge controller?
Thanks
Using a Weize 1210012V Deep cycle GEL battery with 75/15 and 2 100W panels wired in parallel.
Cycle Use: 14.1-14.1
Standby Use: 13.5-13.8
What should the setting be on the charge controller?
Thanks
Absorption 14.1
Float 13.5
Thank you. Been looking for hours all I had to do was this. thanks!