VM-3P75 CTs too small

Is there any possibility to get bigger CTs for the VM-3P75 energy meter?

I can´t work with an EM530 in this case because i just have Ethernet for the energy meter.

This will not work. You have to use a single wire and not the complete cable with L, N and Gnd

This is single wire. There are 3 of them on a 63A Fuse.

You need to strip the YMVK cable i.e. remove the gray outer insulation and put the CT clamp over the brown wire (which sometimes is black by the way) as shown here:

Also. You may need the usual grey conduit, properly secured to the wall like every 30-50CM (depending on the orientation).

Note: do NOT strip the brown/black wire!

Currently there are no other CTs available but as far as I know there is something in development.

I can´t strip anything here. Thats a three phase System. I have 5 of this cables. Grey, black and brown are L1, L2 and L3. Every single cable is too big to get a CT on it.

Danke Matthias. Also aktuell keine Chance das mit den VM3P75 auszuführen. Das stellt mich vor große Probleme

Aha. Ok. Sorry. Was still early for me. We here are used to the grey multi-core cables. Also used for 3 phase systems. Like 5 x 6 mm² or 5 x 16 mm²

You could use an Ethernet to RS485 converter but I’m not sure if the GX would properly recognize the meter in that case.
If there’s an option for the Ethernet cable to be patched through to the GX, you could run RS485 over it.

Maybe press the wire flat a bit, so it becomes more oval instead of round ?

As a last option, if the cable is just a tiny little bit too wide for the current clamp, would be to cut away the inner plastic of the current clamp.
This would obviously void the warranty of course.

I was very disappointed when my VM-3P75CT arrived with the small CTs. Following some research, I crossed the Victron supplied numbers (Tokin C-CT-0810-05-01) to a 3000:1 datasheet. Then I found a 80-C/CT-1216 from Mouser electronics. I spliced some extension wire to end up with about the same length and my meter is in business. Yes - I can’t call it Victron calibrated, but it does compare nicely with my installed Scheider system. The Victron energy meter is very responsive. Consider me a satisfied customer (now).

I’ll have a look at the 80-C/CT-1216, thank you.

I had the same problem as most people have I guess with these clamps that they don’t fit standard 25mm meter tails unless you strip the outer insulation layer. This is fine inside a consumer unit but not an option if you need to do it external to one. The only other option is placing the clamp inside another small enclosure where you strip the outer insulation if it is exposed which probably isn’t ideal. Hopefully they’ll release a larger version.

@All The new VM-3P5A should be available in a few weeks.
It can be used with any standard 5A CT.

Never mind that @M_Lange Victron need to allow us to assign the other CT’s to other devices I keep asking @guystewart for this addon, as my other CT’s are just in the box not used.

Should be possible via SW but as far as I know there is no timeline for that right now.

A known feature request!

I would like it myself, the team is aware but no further information at this stage.