Victron Wallbox not charging in Auto mode: “Waiting for sun” – ERROR

Hello,

My Victron Wallbox won’t charge in Auto mode and constantly displays “Waiting for sun”, even though there’s plenty of surplus power!

I happened to come across this error in the Modbus settings. I can delete it, but it then reappears automatically!

Charging in “Manual” mode works!

A quick overview of my system:

  • Victron Multplus2 with Cerbox GX and Pylontech batteries
  • Victron VM-3P75CT EnergyMeter
  • Victron Wallbox
  • Huawei inverter for the 17 kWp rooftop PV system, with its own energy meter

I can see in VRM that there’s surplus power! The values are negative and, during testing, well over 6–7 kW.

Controlling the Wallbox via the CerboGX seems to work.
For example, when I change the mode, the Wallbox accepts it!

I also had the Home Assistant integrations for ESS and Wallbox installed, but I’ve now removed them.

Unfortunately, that didn’t help either.

I’m still seeing this error:

Does anyone have any idea how I can fix this?

Could you show a screenshot of the VRM and the EVCS settings?

Is communication between the GX device and the EVCS working, though?
In other words, are the system’s current values shown in the EVCS web interface?

Is the PV inverter being read and displayed by the Victron system?
A negative reading from the grid sensor alone isn’t enough; the EVCS needs to know the PV output.

The PV inverter is not visible in the Victron system.

Communication between the GX device and the EVCS seems to be working. At least the change I make in the settings under “CerboGX->Devices->EVCS” is received by the EVCS.

2026-10-04_21h44_21

I assumed the readings from the Victron VM-3P75CT would be sufficient to detect surplus power.

@M_Lange How should systems that only have 3rd party AC-coupled PV connected via AC-in show their generation on the GX device?

Unfortunately not; the PV output has to be known to the system.
Either the PV inverter must be readable directly via Modbus/Sunspec, or, if that isn’t possible, it must be measured using a separate meter, such as an ET340 or EM540.

@dmajwool

Thanks for the quick reply. But I’m still a little confused :slight_smile: .

Shouldn’t it already know the surplus from the Victron VM-3P75CT EnergyMeter? That’s the actual surplus currently being fed into the grid (if there is any surplus).

If I connect another Energy Meter to the PV line, the CerboGX will get the current PV output, but not the surplus.

Or am I missing something?

The wallbox needs to know how much PV power is available, so this needs to be measured separately.
The negative value from the grid sensor alone isn’t enough.

Can you explain why this PV output figure is needed? What additional information about power available to be sent to the EVCS does it give that isn’t given by the grid meter?
After all , the EVCS balances the grid feed to zero, rather than matching a figure from the PV inverter.

No, I’m not the developer, I can’t explain it even further, I just know that it is like that.

My guess is that the auto mode is based on the available PV energy, not the grid feed-in, because the auto mode can also start charging if there is no grid feed-in because the battery isn’t at 100% or because it is an off-grid system.

The statistics on VRM and the remote console overview are also better if the system knows the PV power.

How does it work?

The EVCS will automatically start charging when the vehicle is connected and the following conditions are met:

  1. The current state of charge is above the 'Start charging at backup battery SoC (%) value.

  2. There is enough excess solar power available, with excess solar power calculated as follows:

    • Excess solar power = Total PV production - AC loads (without car consumption) = 1380W (230V x 6A)

      In the example above, the Min. charge current (from 6A) value has been set to 6A. The required excess solar power increases accordingly if a higher value is set for the Min. charge current (from 6A). Please see the chapter VictronConnect setup, configuration and operation for details on both parameters.

  3. Or, if there is not enough excess solar power available to meet the minimum charge current requirement as per 2., it is possible to enable the ‘Allow low excess solar power for auto mode’ option. This option supplements the required power with additional power from the grid to meet the minimum current requirement. See chapter VictronConnect setup, configuration and operation for details.

I can answer - what if your system is feeding just because the energy price is high and it is confgured to do that in this case? we need to know where the energy is coming from to make sure it is from PV.

Interesting. Is that because in this case you don’t want to export “brown” energy?