Victron ESS – Grid feed-in and central grid and system protection concerns during registration
Hello everyone,
I retrofitted a Victron battery storage system to my PV installation. My grid operator has raised a few concerns during the registration process. Perhaps someone has had a similar problem and can help me.
My system:
-
PV inverter: Huawei SUN2000-30KTL-M3, 30 kVA, three-phase
-
Battery inverter: Victron MultiPlus-II 48/5000/70-50 GX, single-phase on L1
-
Energy meter: EM24, three-phase
-
ESS mode: Optimised without BatteryLife
-
Battery: approx. 16 kWh LiFePO4
-
PV system: surplus feed-in
The Victron is only intended to increase my self-consumption. So the battery should not feed any energy into the public grid. The PV system can, of course, continue to feed surplus electricity into the grid.
1. Feed-in from the battery
Section 4.10 of Victron’s manufacturer’s declaration dated 14 November 2024 states that electricity charged into the battery from the public grid is not fed back into the grid.
My grid operator objects that it does not say whether feed-in of stored PV electricity is also prevented.
My questions:
-
Does the Victron ESS generally prevent electricity from the battery being fed into the grid?
-
Does this also work during rapid load changes or if the connection to the EM24 fails?
-
Is there any official confirmation of this from Victron?
2. Phase imbalance caused by the Victron
My Huawei inverter feeds power into all three phases evenly, up to a maximum of 10 kVA per phase.
The Victron is also connected to L1.
Since I use three-phase summation control, the Victron can supply power on L1 to balance consumption on L2 and L3.
My grid operator is therefore concerned that the total feed-in on L1 could exceed 10 kVA.
My questions:
-
Could this actually happen during normal ESS operation?
-
Is there a setting that would let me limit the total feed-in on L1 to a maximum of 10 kVA?
-
Could I still use three-phase summation control?
-
Alternatively, would it be possible to apply such a limit via Modbus or an external controller?
I would also be happy for the Victron to reduce its output, even if that means drawing some grid power on L2 or L3.
3. Central grid and system protection
My Huawei inverter already has a capacity of 30 kVA. Because of the additional Victron, my grid operator is therefore requiring central grid and system protection.
According to the grid operator, this might not be necessary if I can prove that the Victron battery storage system does not feed electricity into the grid.
My questions on this:
-
Has anyone registered a similar Victron battery storage system without central grid and system protection?
-
Can the Victron ESS be considered a “storage system without grid feed-in” under VDE-AR-N 4105?
-
Is there any relevant documentation or manufacturer’s confirmation from Victron?
I would like to continue operating my Victron with three-phase summation control without having to retrofit additional central grid and system protection.
Perhaps someone has experience with this or an idea of how I could solve the problem.
Many thanks in advance for your help!