Victron ESS – Registration issues due to grid export and grid protection

Victron ESS – Grid feed-in and central grid and system protection concerns during registration

Hello everyone,

I retrofitted a Victron battery storage system to my PV installation. My grid operator has raised a few concerns during the registration process. Perhaps someone has had a similar problem and can help me.

My system:

  • PV inverter: Huawei SUN2000-30KTL-M3, 30 kVA, three-phase

  • Battery inverter: Victron MultiPlus-II 48/5000/70-50 GX, single-phase on L1

  • Energy meter: EM24, three-phase

  • ESS mode: Optimised without BatteryLife

  • Battery: approx. 16 kWh LiFePO4

  • PV system: surplus feed-in

The Victron is only intended to increase my self-consumption. So the battery should not feed any energy into the public grid. The PV system can, of course, continue to feed surplus electricity into the grid.

1. Feed-in from the battery

Section 4.10 of Victron’s manufacturer’s declaration dated 14 November 2024 states that electricity charged into the battery from the public grid is not fed back into the grid.

My grid operator objects that it does not say whether feed-in of stored PV electricity is also prevented.

My questions:

  • Does the Victron ESS generally prevent electricity from the battery being fed into the grid?

  • Does this also work during rapid load changes or if the connection to the EM24 fails?

  • Is there any official confirmation of this from Victron?

2. Phase imbalance caused by the Victron

My Huawei inverter feeds power into all three phases evenly, up to a maximum of 10 kVA per phase.

The Victron is also connected to L1.

Since I use three-phase summation control, the Victron can supply power on L1 to balance consumption on L2 and L3.

My grid operator is therefore concerned that the total feed-in on L1 could exceed 10 kVA.

My questions:

  • Could this actually happen during normal ESS operation?

  • Is there a setting that would let me limit the total feed-in on L1 to a maximum of 10 kVA?

  • Could I still use three-phase summation control?

  • Alternatively, would it be possible to apply such a limit via Modbus or an external controller?

I would also be happy for the Victron to reduce its output, even if that means drawing some grid power on L2 or L3.

3. Central grid and system protection

My Huawei inverter already has a capacity of 30 kVA. Because of the additional Victron, my grid operator is therefore requiring central grid and system protection.

According to the grid operator, this might not be necessary if I can prove that the Victron battery storage system does not feed electricity into the grid.

My questions on this:

  • Has anyone registered a similar Victron battery storage system without central grid and system protection?

  • Can the Victron ESS be considered a “storage system without grid feed-in” under VDE-AR-N 4105?

  • Is there any relevant documentation or manufacturer’s confirmation from Victron?

I would like to continue operating my Victron with three-phase summation control without having to retrofit additional central grid and system protection.

Perhaps someone has experience with this or an idea of how I could solve the problem.

Many thanks in advance for your help!

I’ll answer you as a bit of a techie; I can’t tell you much about the bureaucratic side of things:

  1. In principle, the Multi can feed in as much or as little as you like; it all depends on the settings you want. If you run it purely as an ESS, though, it only operates for self-consumption using the configured setpoint (which can be 0, but can also be slightly negative or positive).

I’d point the grid operator to the upcoming flat-rate option under § 19(3c) EEG, which means that distinguishing between grey and green electricity will no longer be necessary up to a certain annual share. I’d put it diplomatically: there’s no need to make an issue of it now if it’s expected to make no difference from 1 January (given your system size).

  1. Have a look at the MP certificates on the website. According to the certificates, the devices meet the requirements of VDE-AR-N 4105. The appendix lists a maximum active power of 4.20 kW and a maximum apparent power of 4.39 kVA for the 48/5000.

Here I’d simply argue that the device has all the certifications required for the German market and single-phase operation, so it’s reasonable to assume that the authorities have signed off on all of this too.

  1. This will be difficult to demonstrate; see 1: the MP will do (or not do) whatever you tell it to. So if you don’t have an installer who can lock the settings via installer access, you could configure it however you like — and, of course, change it again after the inspection.

Here I’d simply assure the grid operator that, as an end consumer who pays grid fees, you have absolutely no financial interest in sending electricity drawn from the grid back into it :grimacing:

Thank you very much for your reply!

On point 1:

My PV system now has a capacity of 51.7 kWp and is split between two operators. As far as I understand it, I therefore cannot use the flat-rate option.

On point 2:

The point about the 4.39 kVA is a good one. So the phase imbalance caused by the Victron itself shouldn’t actually be a problem.

However, my grid operator still has concerns about the following rather unrealistic scenario:

  • The Huawei is running at full power and generates 10 kW per phase (assuming cos φ = 1 for simplicity).

  • There is no consumption on L1.

  • 17 kW is consumed on each of L2 and L3.

  • This means that 10 kW is already being fed into the grid on L1, while 7 kW is drawn from the grid on each of L2 and L3.

  • This results in a total grid import of 4 kW.

With three-phase sum regulation, the Victron would try to compensate for this 4 kW grid import. Since the Victron is connected to L1, a total of 14 kW would be fed into the grid on that phase.

Although the EM24 would measure 0 W in total, 14 kW would actually be fed into the grid on L1, while 7 kW would be drawn from the grid on each of L2 and L3.

Is there a way to dynamically limit the total feed-in on L1 (Huawei + Victron) to a maximum of 10 kVA?

In this case, the Victron would have to reduce its discharge power or stop discharging altogether. I would have no problem with this resulting in continued grid import.

However, I would generally like to keep three-phase sum regulation enabled.

On point 3:

My grid operator refers to VDE-AR-N 4105 in requiring central NA protection. However, this standard provides an exception for storage systems without grid feed-in, even if the combined inverter capacity of the PV system and storage exceeds 30 kVA.

I spoke to my grid operator again yesterday. In principle, they have no problem approving the storage system without additional central NA protection.

I simply need to be able to demonstrate technically that the MultiPlus does not feed battery energy into the grid—even in the rather unrealistic example in point 2.

Of course, I have no intention of feeding electricity from my battery into the grid. Unfortunately, that assurance is not enough for my grid operator.

So what I mainly want to know is how I can reliably prevent feed-in by technical means and demonstrate this to my grid operator.

Thanks again for your help!

I suspect this might help you.

Limiting the AC export current per phase. In your case, that would be 10000W/230V ~ 44A

PERFECT!

I think that’s exactly the approach I was looking for.

Do you happen to know whether there’s also an official statement or certificate from Victron about this?

I find it a little strange that this topic has hardly been discussed so far and that there appears to be no official statement from Victron about it.

The VDE-AR-N 4105 is actually quite clear on this point. Each grid operator can set additional requirements in its own TAB, but if it refers to VDE-AR-N 4105, it must also take the exceptions listed there into account.

Accordingly, under certain conditions, storage systems that do not feed electricity into the grid are also permitted in addition to a 30 kVA PV inverter without central grid and system protection.

This means that you can make full use of a 30 kVA PV inverter (depending on the orientation, 60–70 kWp is conceivable here) and also connect additional PV modules to the Victron battery system via MPPT charge controllers.

With an average feed-in tariff of around 6.3–6.4 euro cents/kWh for 60–70 kWp, that adds up to a good €50,000–60,000 over 20 years from the feed-in tariff alone.

Surely this system configuration must be of interest to many Victron users, especially if it means they can avoid installing additional central grid and system protection.

Sorry, unfortunately I don’t know either.

Unfortunately not — it’s a blanket technical limit designed for overload protection.

I think 5A is the lowest value, and it would also prevent the MP from feeding in more than 5A in permitted phase-imbalance ranges.

If you have more than 50 kW of PV, my recommendation would be to build a three-phase Victron system.

Either 3 x 3000, but since the 5000s aren’t that much more expensive now, I’d go with those.

Of course the grid operator is right, and example 2 could lead to excessive overall phase imbalance — but they’re taking it a bit too far, because the phase-imbalance rules apply to individual devices. Never to the sum of potentially possible combinations. Otherwise, every combination of awkward hob and oven use while the wife is also blow-drying her hair on L1 would be a problem. Add a single-phase electric car on L1 and… well…

Requirements at the level of actual loads really only apply to business customers.

OK, maybe I’m misunderstanding, but isn’t that exactly the function I need? I can enter 43A (9,890 VA) as the maximum system output current. This prevents any phase from feeding more than 43A into the grid. As soon as one phase tries to feed more, the ESS reduces battery discharge (or solar production, if PV modules are connected).

Of course, this is only a configurable control limit, not a hard shutdown limit. That’s why I’m still looking for something official from Victron.

Yes, exactly, that’s what it’s intended for. However, it doesn’t prevent load imbalance in downstream areas. It’s purely a protective setting to prevent fuses from tripping or cables from overheating.

The phase imbalance is irrelevant with an MP 5000, since it can generate a maximum of 4.39 kVA, which is below the 4.6 kVA limit. The Huawei inverter distributes its feed-in equally across all three phases. So the maximum difference between the phases can only be 4.39 kVA.