Hi guys, first time posting on here, I usually manage to sort things without too much trouble, but I seem to have an issue that has me stumped.
I have put it down as DIY, I am not an installer/professional, neither an expert - but I do have good energy management and electronics design experience.
I have used a MultiPlus-II 48/5000 for over a year without issue.
I wished to increase the charge rate on the batteries, and had the opportunity to get another MultiPlus-II 48/5000
All the obvious has been done, similar serial numbers, updated to have the same firmware etc. VE Bus setup complete so that one is master and the other slave. I have an external (Victron) CT around the meter tails (unchanged since running a single unit).
But I am seeing odd power readings on the Cerbo. This started as soon as I installed the second unit - perfect before hand.
A ‘real’ grid meter actually shows grid power as zero - which is also the set point… so ‘correct’.
From the above, the 3570W is feeding nominally 2200W to the batteries, and the remaining nominally 1200W to the AC side.
The load is actually around 1200W at this point.
So, physically, the values add up, but the Cerbo is thinking 650W is going back to the grid when it is in fact going to the load.
As I say, it has a physical CT on the grid supply, so the reading should be right.
I am mostly sure that the AC supply and load are always split 50/50 in the display. This leads me to think there is some odd divide by two (due to the two units running in parallel) - though that isn’t proved yet.
Two easy questions;
When setting up, I find it odd that you have to install the ESS on both MultiPluses - I would have expected the master to transfer this - but no issue as long as my understanding is corrects. So, could someone confirm that this is the case, and ESS does need to be installed on both ‘manually’? It seems a receipe for disaster as you could set different battery sizes etc and really mess things up if you tried.
The second trivial question is, when setting up the first, obviously the external CT is selected. I have assumed that on the second, external CT should NOT be selected on the basis that IT doesn’t have one… but it is ambiguous as overall, the system does.
Any ideas would be most appreciated as I am not quite sure what to look at next.
Thanks