I have an issue.
Running ESS.
I had a single 48/3000 multiplus 2 and this would work great. It would maintain the 50w on the grid and try to put all of the grid connected PV towards battery charging.
I had excess PV due to the limitations of the multiplus 2 charging at its max.
So to increase the charging capacity to try and use all the grid connected PV and export as little as possible, I got another 48/3000 MP2.
They are setup in parallel, with identical AC lengths and identical DC lengths etc.
But it now looks like the MP2’s are not evenly trying to charge the battery. I am actually now exporting more to the grid than I was originally, and the batteries and not being recovered.
I have 2 x ET112 meters, one on “Grid Metering” and one on the “Grid connected PV”.
I also have an external Victron CT (CTR12) to monitor loads.
To me it looks like:
The MP2’s are trying to share the charging, but only 1 is actually charging (so only using half the available Grid Connect Solar). I need to be home during the day to put a clamp meter on the DC side of the inverter.
I have nothing limited in the charging or inverting and no DVCC set up.
I have tried DESS On and Off, in Green mode ETC, and no difference.
Screenshot_20250903_103130_Chrome1080×2121 155 KB
1 x 48/3000/35-32 GX
1 x 48/3000/35-32
Just to add another weird issue.
If i set the Grid Current Limit to 16A, for example, the max I can draw from the grid is ~8A. This is doing the exact opposite to what i thought 2 in Parallel is meant to do. (3A on 6A, 5A on 10A, ~6A on 13A, 16A on 32A setting ETC)
Anyone seen this? Could it be a firmware bug.
It is running the latest official release.
Also i have seen conflicting information on what you do with the current sense of the slave unit do you have it connected or just remove it completely?
Cheers.
Red.