Soft-Bricked Multiplus One with vrm Controls?

Hi All
I have a Multiplus 12/1600/70 that I took out of service today by changing its state to “off” using the IOS Vrm app Controls. This took down my AC, and internet. Now vrm has no access to turn it back on. Turning the hard switch to both Charge and On caused the LEDs on front to blink on, then go dark. No sounds of relays etc.

Is there a way to make the physical switch take priority without computer access?

Hoping there is a quick resolution for me.

Thanks
AM

Unplug the cerbo vebus cable and try turning it on again.
Or, connect to the built in AP on the Cerbo and access the console that way to change the settings.
Process is in the manual.

Disable realtime updates in VRM and you won’t be able to turn the system on or off remotely from it.

No need to do that, inverter control is a separate option in VRM. It is off by default, it has to be enabled.
In the same way VRM asks you to confirm your choice on switching.
Pays to have a DC backup for wifi if you’re doing remote work, just in case.

Indeed, although it reduces the overall risk of the other setting being adjust by mistake by removing the temptation :slight_smile: At least there is flexibility.

Thanks all for your help!
Nicks response was the kick I needed.
The one detail is that the cerbo console also wasn’t available since it was connected to the same unavailable network, and its not available via the bluetooth connection either.

I ran the networking stuff directly to shore power for a moment to bring the network back up, then changed the Multiplus, then put everything back in place.

Sounds like the newer ones may solve this but baffled there isn’t an obvious “Transparent” setting that lets you keep your lights on while you figure out whats going on.

Thanks
A