At first, I was pleased to finally get a smart meter gateway and to be able to switch to billing every 15 minutes soon…
But since it was installed, something has gone completely wrong. The VM-3P75CT, which had previously been measuring perfectly, no longer works properly.
Either: I’m seeing consumption of between 4 and 7.3 kW on two phases where there isn’t any consumption at all, which led to the batteries being discharged overnight, as if I had an electric car plugged in.
Or: I’m seeing 0 W on one phase, even though there are appliances connected to it (see screenshot).
Has anyone experienced this problem? Unfortunately, I haven’t been able to find anything about it.
Many thanks
One could ask a lot of follow-up questions and make assumptions at this point, but the simplest thing would be to first check whether the colleague installed anything incorrectly or differently when replacing the meter.
So, check that the instrument transformers and voltage inputs are assigned correctly, and that the transformers are the right way round. An error in the phase sequence would be flagged by a three-phase system.
Hi Denni, thanks. I don’t think that’s the cause, … I suspect EMC interference, … maybe the LTE cable or the antenna? Or perhaps communication via powerline (PLC)?
The meter cabinet is new — it only had an electrical meter that was too large. The gateway apparently communicates with the meter only via an infrared interface and isn’t connected to the cable at all. It also sends everything via LTE — in any case, the cabinet now has an antenna on top. The transformers are definitely the right way round — I checked that. In my opinion, a changed phase sequence wouldn’t explain the periodic interference every 30 minutes — or would it?
I’d rule out the phase sequence.
Are the current transformer clamps also fully and properly closed?
To rule out Powerline, you could temporarily connect to the VE.Bus with a long patch cable.
But I’m only guessing; I haven’t come across this phenomenon before. It’s strange that it occurs sporadically.
You could check whether the output power values of the Multi units are plausible—in other words, whether the values were transmitted incorrectly or the system responded incorrectly.
Are the power fluctuations rapid and extreme? Maybe the connections for the external sensors on the Multi units?
Did it start occurring directly after the Gateway was installed?
Hi Denni, the patch cable doesn’t work. It’s too far away. I think the consumption readings are nonsense and that the ESS is misinterpreting them, eventually even discharging and feeding power into the grid. I would trust the SmartShunt. The battery was only showing 26% in the mornings. For now, I’ve switched the grid measurement setting in the console to inverter/charger to prevent it from discharging. But that’s not a real solution.
It appeared immediately after installing the gateway. At first, I also thought the measuring clamps had been installed incorrectly. I haven’t changed a thing on the Multis.
If you have all the loads connected to ACout, you could try configuring the Multi sensors as grid meters.
If not, you could still try setting it that way and see whether the system then behaves calmly.
…but I really don’t have any good ideas either about what might help in the short term. You can’t switch off the gateway, can you?
No, you can’t just turn off the gateway that easily.
@hironimus76
Have you made any progress with this?
I’ve had the same gateway installed for a few days and was planning to install the VM-3P75CT soon.
S.
the smart meter doesn’t have VE.Bus, but a CAN bus!
Bye
You’re right.
Could it be that you haven’t enabled the ESS assistant in every MultiPlus? :wink:
I think the problem is probably moot by now—but it would still be great to hear from @hironimus76 what the problem was, or what solution they ultimately found! (I’m assuming it’s no longer an issue.)