My system consists of 4 Smart Lithium Batteries 12V 330Ah in parallel, Lynx Smart BMS 1000 and Quattro 5KW in combination with 5 Smart Solar MPPT chargers and a 11kW Genset.
When my SOC is around 70% and I start the Generator, the charging current only goes up to about 40A. Absorbtion voltage is set to 14.2V, float 13.5V. Generator is connected to AC1 and AC1current limit is set to 30A, AC devices like water heater and cooker are working properly.
Any idea how I can increase the charging current?
Thanks, Axel
If you read section 6.3 of the manual, the BMS only charges at the float voltage after a complete absorption until the SOC dips below 70% or after 30 days. These are the repeat absorption interval and SOC threshold. Increase the SOC threshold.https://www.victronenergy.com/media/pg/Lynx_Smart_BMS/en/configuration-and-settings.html#UUID-2a3623df-8422-a501-03ef-345bd8f0982a
That has worked fine, thank you!