Greetings all.
I have an all-Victron electrical system in my van configured with:
- 2 x 12V Smart Lithium 200Ah connected in parallel
- Lynx Smart BMS
- Smart Battery Protect connected to ATD output of Lynx
- MultiPlus 2000
- Cerbo GX
I recently had my van serviced and although the technician shut off the main battery switch, the batteries dropped below their ATD voltage. At the point the battery protect relay must have disconnected. However, there appears to be some parasitic drain in the system because when I went to pick up the van the voltage on the lithiums was down to 5.6V.
I disconnected the battery cabling and connected a power supply to the terminals of the first battery, set for constant current charging at 0.1A. Over the course of a few hours the battery rose to 10V, with a variation between the cells of only 0.06V. I will now do the same to the second battery.
So far, so good. However, in looking ahead to the next steps in section 6.1.5 (“Battery very low terminal voltage”) of the battery manual, I am wondering how best to proceed:
The manual says to increase the charge current to 20A (0.1C) at 13.8V. Can I do this using the MultiPlus and Lynx that are currently in place? The MultiPlus’s bulk charging voltage is 14.2V, but I should be able to adjust this — and the max charge current — using Victron Connect. If I do so, will the BMS in the Lynx properly manage disconnecting the charger as need for cell balancing? The Lynx manual says that its charge profile is not configurable, so I’m not clear on whether it will somehow interfere with the charging/balancing process. (I assume I also need to reconfigure the Lynx’s bank capacity setting since I will only be charging one battery at a time.)
Thanks in advance for your advice.