PV power going to the grid instead of the battery?

I installed a Victron ESS at some acquaintances’ place over the summer.

3x Multiplus 48/5000 connected to 6x Pylontech US 3000.

This morning, it was noticed that despite PV power being available at > 200W, the surplus is being fed into the grid instead of charging the battery. See pictures.

Why?

The batteries are in the utility room, where the temperature is constantly >15°C.

Looking back, I saw that the battery also only started charging after a delay over the past few days.

Hi,

Your MP is showing external control. I would guess that one is telling the battery not to charge. How are you controlling the MP? Pylon BMW or something external (home assistant, modbus, …)

It is controlled via a Cerbo, which receives its information from a VM-3P75 over the VE-Can bus.

There’s a message ESS #1… it could be that the battery is sending an error ..

When was it last at 100%?

Have you enabled Battery Life?

Could you provide more information about your settings?

The last time it was at 100% was yesterday at midday; Battery Life isn’t active.

What settings/information are needed?

Is DESS switched on, yes or no? What are the DESS settings in VRM when it’s on?
Why isn’t BatteryLife enabled?
Have you selected the correct BMS in the Cerbo?

DESS is not active; BMS in the Cerbo is the right setting. I think BatteryLife is unnecessary for this installation, as there is enough PV available.

Basically, it works without any problems. The only thing I noticed was the delay in the morning before charging starts.

The AI said that it’s a protection function which, through a generous hysteresis, prevents switching on and off too frequently, thereby avoiding premature relay wear.

But ESS, yes? And is the assistant installed on all MP II units?

What is set as the grid setpoint?

Yes, the ESS assistant is installed on all 3 MPs.

Grid setpoint is 0 W.