I installed a Victron ESS at some acquaintances’ place over the summer.
3x Multiplus 48/5000 connected to 6x Pylontech US 3000.
This morning, it was noticed that despite PV power being available at > 200W, the surplus is being fed into the grid instead of charging the battery. See pictures.
Your MP is showing external control. I would guess that one is telling the battery not to charge. How are you controlling the MP? Pylon BMW or something external (home assistant, modbus, …)
Is DESS switched on, yes or no? What are the DESS settings in VRM when it’s on?
Why isn’t BatteryLife enabled?
Have you selected the correct BMS in the Cerbo?
DESS is not active; BMS in the Cerbo is the right setting. I think BatteryLife is unnecessary for this installation, as there is enough PV available.
Basically, it works without any problems. The only thing I noticed was the delay in the morning before charging starts.
The AI said that it’s a protection function which, through a generous hysteresis, prevents switching on and off too frequently, thereby avoiding premature relay wear.