Hi,
yes, the MP2 configuration in VEConfigure really is old-school. I felt like I was back in Win98 too, in terms of the program design… I use the Cerbo GX as the control unit (more connections, etc.; it’s proven its worth).
Best regards
OK, so the problem is mostly solved. My pet sparkie had plugged a CANbus lead into a VEbus port. Swapped them around and hey presto! it nearly works.
Despite everything I tried, I can’t get the system to see the VM-3P75CT over CANbus. I connected via ethernet and VictronConnect now sees it as a local device, but it doesn’t show in VRM portal as part of my installation. If I tell the GX to use the external meter, it just goes to pass thru and says it can’t find one. Any ideas?
If the meter is connected via Ethernet, Modbus scanning must be enabled in the GX.
SETTINGS->INTEGRATIONS->Modbus Devices->Automatic Scanning = True
Perfect, thanks!
As an additional option, you can also configure the system so that it doesn’t require an external meter. However, this setting only ensures that if you connect something to AC Out, at least that part is powered by the battery. Otherwise, as you’ve already described, the system switches to bypass mode in general.
System → ESS grid meter required.
As long as the meter is available, though, the system will use it and also cover loads on AC In.
Glad you got it sorted over LAN. If you’re using the Can connections, make sure you’re using the Terminators too.