Hello, what options are available for implementing the network operator’s new „active power setpoint“ requirement (Austria) in an ESS configuration?
Essentially, the network operator needs the ability to remotely set the feed-in via an LSG (= load switching device / ripple control receiver) to zero, e.g. when too much power is being fed into the grid.
The LSG switches a contact (normally open), which then has to be connected via an interposing relay to all generating systems so that the feed-in can be set to 0.
Unfortunately, I only recently became aware of this new requirement. However, I am already in the final phase of wiring and commissioning my system, which has the following main components:
- 1x Cerbo GX 2 plus display
- 3x MultiPlus 2 48/5000 → in a 3-phase configuration
- 1x Smart RS 450/200
- 16S batteries controlled via CAN BMS
- Lynx
- 3-phase microinverters from Hoymiles
Simplified representation of the system’s AC configuration:
Meter distribution board downstream-of-meter fuse → sub-distribution board AC-in of the 3 Multis → all loads and microinverters are connected (with the appropriate fuses/RCDs) to AC Out 1 of the 3 Multis. The Multis can be bypassed in the event of servicing by means of a „Grid-0-Emergency“ bypass switch. Normally, the switch is always set to „Emergency“.
What options are available for implementing this remotely controlled zero-export function in an ESS configuration?
One approach would be to use „ESS in Mode 3“ to set „Feed-in“ to zero, triggered via an interposing relay!?? Does that work? Are there any other approaches that have already been tested in practice?
Once the feed-in restriction is lifted again (= the LSG signal is no longer active), the ESS should function normally again and be able to feed power into the grid.