Hello everyone,
My ESS system has been doing something strange for several years, and I think I’ve now found the cause. Perhaps someone else has encountered this, or even has a solution.
System:
- 3x MultiPlus-II 48/3000/35-32, three-phase,
- Cerbo GX, Venus OS v3.66
- ESS, Optimized without BatteryLife, grid setpoint -20 W, grid meter connected to the Cerbo
- Grid Code VDE-AR-N 4105:2018-11 (internal NS protection), LOM B
- All loads on AC-In, AC-Out unloaded
- PV via external inverters (SMA, Hoymiles) on the grid side
What happens:
Several times a day, especially in the evening and at night, the system suddenly stops discharging. Battery power drops from a few hundred watts (or a few kW) to around 0 W, and sometimes it even charges briefly at 200–300 W. The grid then takes over the entire household load. After a few seconds to around 2.5 minutes, discharging resumes at its previous level. No alarm, no Grid Lost, no 60-second reconnection.
What I’ve found:
I log the system every second via Modbus TCP in Home Assistant. The AC-In frequency reported by VE.Bus is normally stable at 50.1 Hz. During these dropouts, it jumps on all three phases between 49.59 / 49.85 / 50.36 / 50.62 / 50.89 Hz. My external grid meter shows 50.0 Hz throughout, so this isn’t an actual frequency deviation.
My DSO (FairNetz, Reutlingen area) sends ripple-control telegrams at 383.33 Hz. The frequency jumps coincide exactly with the telegrams. Over 10 days, I counted 529 such periods. Most start 3–5 s after a quarter-hour mark and have very consistent durations (e.g. 22:30 always around 142 s, 06:00 around 99 s, 21:00 around 75 s). There are also dusk- and dawn-dependent telegrams in the morning and evening (street lighting).
The DSO kindly sent a test telegram at a time when nothing normally happens (25.11., 20:40):
- 20:40:03–20:40:08: frequency jumps on all three phases
- 20:40:06: battery goes from -400 W (discharging) to +280 W (charging), grid import rises to around 480 W
- 20:40:18: discharging resumes, around 10 s after the last frequency jump
- Otherwise, nothing unusual at all between 20:30 and 20:50
I’m therefore fairly sure that the ripple-control signal is the trigger. The DSO measured the signal level near my home: well below 4 V, so it’s within the permitted range. So the problem isn’t with the grid. My theory is that the Multi determines frequency from the zero crossings without much filtering, and a few volts at 383 Hz shift the zero crossings by a few tens of microseconds. That produces exactly these jumps of around 0.26 Hz. Values above 50.2 Hz might then trigger the overfrequency power reduction P(f) under VDE 4105, with a hold time of around 10 s. Since all loads are on AC-In, from the Multi’s perspective every discharge counts as feed-in. But this is just my theory.
The Multis also respond during daytime charging, by the way, but only with brief dips of around 1 kW per pulse.
A second Victron system in the same area (with a different owner) shows the same behaviour at the same times.
My questions:
- Has anyone else experienced this with ripple control, in Germany or elsewhere?
- Which function is responding here: P(f), LOM, ROCOF or something else?
- Is there a VE.Bus firmware version with better filtering of the frequency measurement, or is this planned?
- Is there a setting that would help without sacrificing VDE-4105 compliance?
I’m attaching two graphs (test telegram and a normal telegram around 22:30). I’d be happy to share the complete logs and the list of telegram periods if anyone from Victron would like to take a look.
Thanks and regards,
Martin