MultiPlus-II ESS interrupts discharge during ripple-control signals (383.33 Hz)

Hello everyone,

My ESS system has been doing something strange for several years, and I think I’ve now found the cause. Perhaps someone else has encountered this, or even has a solution.

System:

  • 3x MultiPlus-II 48/3000/35-32, three-phase,
  • Cerbo GX, Venus OS v3.66
  • ESS, Optimized without BatteryLife, grid setpoint -20 W, grid meter connected to the Cerbo
  • Grid Code VDE-AR-N 4105:2018-11 (internal NS protection), LOM B
  • All loads on AC-In, AC-Out unloaded
  • PV via external inverters (SMA, Hoymiles) on the grid side

What happens:
Several times a day, especially in the evening and at night, the system suddenly stops discharging. Battery power drops from a few hundred watts (or a few kW) to around 0 W, and sometimes it even charges briefly at 200–300 W. The grid then takes over the entire household load. After a few seconds to around 2.5 minutes, discharging resumes at its previous level. No alarm, no Grid Lost, no 60-second reconnection.

What I’ve found:
I log the system every second via Modbus TCP in Home Assistant. The AC-In frequency reported by VE.Bus is normally stable at 50.1 Hz. During these dropouts, it jumps on all three phases between 49.59 / 49.85 / 50.36 / 50.62 / 50.89 Hz. My external grid meter shows 50.0 Hz throughout, so this isn’t an actual frequency deviation.

My DSO (FairNetz, Reutlingen area) sends ripple-control telegrams at 383.33 Hz. The frequency jumps coincide exactly with the telegrams. Over 10 days, I counted 529 such periods. Most start 3–5 s after a quarter-hour mark and have very consistent durations (e.g. 22:30 always around 142 s, 06:00 around 99 s, 21:00 around 75 s). There are also dusk- and dawn-dependent telegrams in the morning and evening (street lighting).

The DSO kindly sent a test telegram at a time when nothing normally happens (25.11., 20:40):

  • 20:40:03–20:40:08: frequency jumps on all three phases
  • 20:40:06: battery goes from -400 W (discharging) to +280 W (charging), grid import rises to around 480 W
  • 20:40:18: discharging resumes, around 10 s after the last frequency jump
  • Otherwise, nothing unusual at all between 20:30 and 20:50

I’m therefore fairly sure that the ripple-control signal is the trigger. The DSO measured the signal level near my home: well below 4 V, so it’s within the permitted range. So the problem isn’t with the grid. My theory is that the Multi determines frequency from the zero crossings without much filtering, and a few volts at 383 Hz shift the zero crossings by a few tens of microseconds. That produces exactly these jumps of around 0.26 Hz. Values above 50.2 Hz might then trigger the overfrequency power reduction P(f) under VDE 4105, with a hold time of around 10 s. Since all loads are on AC-In, from the Multi’s perspective every discharge counts as feed-in. But this is just my theory.

The Multis also respond during daytime charging, by the way, but only with brief dips of around 1 kW per pulse.

A second Victron system in the same area (with a different owner) shows the same behaviour at the same times.

My questions:

  1. Has anyone else experienced this with ripple control, in Germany or elsewhere?
  2. Which function is responding here: P(f), LOM, ROCOF or something else?
  3. Is there a VE.Bus firmware version with better filtering of the frequency measurement, or is this planned?
  4. Is there a setting that would help without sacrificing VDE-4105 compliance?

I’m attaching two graphs (test telegram and a normal telegram around 22:30). I’d be happy to share the complete logs and the list of telegram periods if anyone from Victron would like to take a look.

Thanks and regards,
Martin

I helped an acquaintance install an MP2-3000GX

Oh, he’s on the Fairnetz Reutlingen network.

Your post here prompted me to take a look at his setup, also for 25 November.

You can also see small deviations in VRM (unfortunately, not very clearly).

I downloaded the CSV and had AI analyse it briefly and compare it with your times:

Comparison with your CSV from 25 November:

  • Test signal at 20:40: There’s exactly one outlier in your data, at 20:40:05: output 49.7 Hz, input 50.36 Hz. That falls right in the middle of his window, 20:40:03–20:40:08. From 20:40:18 onwards, everything is back to normal. The whole evening is quiet before and after that.
  • 22:30, around 142 s in his data: Yours keeps jumping from 22:30:13 to 22:32:05; by 22:32:27, it’s quiet again. That matches a window of about 22:30:04 to 22:32:26.
  • 21:00, around 75 s in his data: There are outliers in your data at 21:00:21 and 21:01:06, both within a little over 75 s.
  • Almost all your outliers start a few seconds after the quarter-hour mark, for example at :07, :08 or :12. That also fits his observation of a 3–5 s delay.

Hi kr0815,

Great, thanks for checking and comparing! The fact that it triggers at exactly 20:40:05 with the test telegram at your acquaintance’s place confirms it pretty conclusively.

I’ve since had a look at another Victron system here in Wannweil (an acquaintance’s, also on FairNetz). There too, the test telegram triggered a response at 20:40, but in exactly the opposite direction: the battery was at approx. 0 W at the time, and the house was running entirely on grid power. At 20:40, the battery suddenly started discharging at approx. 850 W (VRM minute average, so the actual peak was presumably higher and shorter), and grid consumption dropped accordingly. A minute later, everything was back to how it was before. I’m attaching a screenshot.

That brings us to four systems in the FairNetz area. And the response apparently goes in both directions: my battery’s discharge drops off, while his kicks in, even though the battery should be idle. The incorrect frequency readings are sometimes above 50.2 Hz, sometimes below (down to 49.59 Hz). So my current theory is that the Multi responds to over- or under-frequency depending on the measured value, i.e. it either reduces or supplies power.

A few more things about your acquaintance’s system would interest me, if you can take another look:

  • Do you also see a response in battery power or grid consumption at those times? Ideally in the evening at 22:30, when the telegram lasts the longest.
  • Which VE.Bus firmware is running on his MP2?
  • Are his loads connected to AC-In or AC-Out?
  • Which grid code is configured? VDE-AR-N 4105 as well?

Thanks!
Martin

I can’t see anything, but I also don’t know whether the VRM Portal’s resolution is high enough here.

2699558

Only to AC-In.

Yes

Thanks! Firmware 558 is fairly recent, while I’m still on 506. The fact that the frequency still spikes during the test telegram for him probably means that an update alone won’t fix it. Good to know before I update.

I’m not surprised that he can’t see anything for the battery in VRM. With one-minute resolution, brief interruptions are easy to miss; that was the problem for me for years too. Was his battery actually discharging at 22:30? If it was idle at the time, there’s basically nothing to see.

Just a quick addition for everyone: FairNetz has since confirmed that the test telegram was just under 10 s long. The ripple control signal level at my connection is around 3 V, so it’s well within the permitted range. Apparently, that’s still enough to interfere with the frequency measurement of the Multis.

Hello,

A 4 V voltage fluctuation can cause a larger power fluctuation if the Multi detects it because it happens to measure at just the right/wrong moment.

Since the ripple control receiver is connected in the meter cabinet upstream of the system, you could simply filter out the 383 Hz signal for the Multi. However, a suitable filter would be quite expensive because of the high currents that have to pass through it!

The simplest option would be a suitable choke that attenuates the signal level to 10–20% or less, but it would also affect the voltage, as it acts as a frequency-dependent impedance! So it mustn’t be too large!

Ideally, of course, you’d use a notch filter for this frequency.

Cheers

Hello Dieter,

I don’t want to “fiddle around” with the network. I’m hoping Victron will look into this and perhaps sort it out with a firmware upgrade if they see this post.

Regards,
Martin

Hello,

the Victron inverters do work, even if there is still room for improvement, at least on the software side. But if I were you, I wouldn’t count on a quick firmware update.

It’s also not certain that your post will be read by the right people who can do something about it. That used to be better.

I’ve also come across firmware bugs, and I always got the answer: “That’s not a firmware bug!”

So I gave up on that a long time ago and look for a working solution myself!

However, there are restrictions here when operating in ESS mode due to the grid code.

It’s simply not that easy to filter out such disturbances while still complying with the regulations! And as you’ve already noticed, the problem here is likely the shift in the zero crossing, because the frequency is measured from the period duration. If this were a frequency measurement, a measurement would take 100s!

Of course, Victron could put a notch filter for the ripple-control frequency in front of the measurement, but that would mean changing the circuitry of the Multis, and that can’t be done with a firmware update.

Bye

Hello Dieter,

Thanks for your detailed assessment.

I’ve also submitted a support request directly to Victron. Let’s see if I get a response.

In my opinion, a company like Victron should take an issue like this seriously.

It’s obviously not an isolated case; many customers simply don’t notice it. …

The ripple control frequencies are well known, and Victron should find a solution.

Regards

Hello,

if you submit a support request, it goes to the dealer who supplied the Multi or the device; otherwise, Victron probably wouldn’t even acknowledge it!

To be honest, I’ve never looked into it, although I once had one in the meter cabinet too. But that was only responsible for switching tariffs at 6:00 and 21:00.

I don’t have any data on that. But I am a little surprised that the signal is transmitted at such a high level. A higher frequency and a blocking filter in the meter might have been a better solution here. But that would also be more heavily attenuated.

Bye