Hello everyone,

I would like to use the multi rs solar with a pylontech us5000 battery, without using a gx device. Is it possible? How to connect the two? Do I need other connection other that the obvious + and - cables?

The installation is off-grid, so nothing on the AC-in side.

Thanks!

Marco

No, you will need a GX device in order to interpret the BMS data, and whilst it is possible to use the US5000b without the BMS connected to the incerter/charger device, its is STRONGLY not recommended, as if the US5000 is over or under charged (by cell voltage, not overall voltage) it can turn off and leave the output open.

1 Like

yes you can use the pylon without the bms comms to a cerbo.

You just have to make sure of the voltage settings, and set your charge voltage to 0.4 lower than the pylon’s spec to avoid overcharge.

I would not advice that too… you could use a raspberry pi with venus os if costs is the problem

1 Like

I’ve used the Multi RS with Pylontech as you said, for a period of time, configuring charge voltages as below.
Not always the SOC will be properly computed by Multi RS, but it will work.

The Pylontech need at least 52.2V to charge to 100%, but the 52V is for allowing a small room for high cell voltages on the final stage of charging. Anyway, the Pylontech will throw a high voltage warning only at 3.6V per cell.

Thank you all for your replies!

I will investigate the matter further and then decide how to proceed.

The reason I would like to avoid using a GX device is to keep the system as simple as possible. I also do not require all the remote controls and data logs the GX seems to provide.

@stok47 without the bms comms to a cerbo, do I need to connect the battery to the multi RS solar (via a CANbus tybe B cable to the VE.CAN ports)?

Do I need a terminator for the remaining ports?

Thanks again!

Marco

Hey Alex,

thanks for your reply! How exactly did you connect the battery to the Multi RS - apart from + and - leads? No other connection i.e. CANbus?

Thanks,

Marco

Can bus wont work since there is no GX, ve can and bms can are two different “protocols”

You dont need to use that, the cerbo can be without internet connection. Also VRM is a nice thing, but its not a requirement.

I also recommend to use a GX device, does not necessarely need to be a Cerbo, due to the BMS. Its also nice to use the local network connection to configure things (granted, those things dont need config if they dont exist)

There wont be any communication between BMS and Inverter. At the very minimum you should use the “Contact” connector on the Pylontechs, which provides ATC/ATD signals, then use those to control the inverter

Yes. Just (+) and (-). No other connection.
Just use 52V and you’ll be fine, because the Pylontechs start to balance from 3.36V per cell.

If you require any form of accurate SOC you would want to install a shunt/BMV, while that is a less expensive option, spending a bit extra for a Pi or appropriate Cerbo would be a better choice and will provide better protection for your battery, which ultimately is the most expensive part.

The logging provides a history, insight into cell imbalances etc, something that helps with any support or warranty request, should one be required in the future.

So, sure you can omit these parts and charge it old-school, but imo you’re losing more than you’re gaining.

1 Like

Thank you everybody for your contribution!

Seeing that you all pretty much advice against an installation without gx, I have resolved to buy one. After all it is only a few hundred € more, and not worth messing with that in the big picture.

I am looking forward to be up and running as soon as possible.,

Thanks again,

marco

I have received all the components I need for this system, I am now confused on how to wire them together! Please help!!

I have a VE Can to Can bus BMS type A cable between the Cerbo GX VE Can 1 (left) and the Pylontech battery A/Can port, and a 568B cable between the Cerbo GX VE Can 1 (right) and the VE Can port on the Multi RS Solar. The second VE Can port on the Multi RS Solar has a terminator:

Could anyone advise me if this is correct?

Many thanks in advance,

Marco

hi no, you will have to wire them to a separate can port (1 or 2) on the cerbo and set the one with the pylontech connect to bms can and that also needs a terminator, setting is explained in victron pylontech manual

so pylon on ve can 1 (with canbus bms setting) and rs on ve can 2

Thank you Marc

I’ll read through the manuals again…

In your picture you have connected both Multi RS and Pylontech to the same VE.Can port. But they both talk different language and use a different port speed.

You need the Cerbo GX as a translator between your Multi RS and Pylontech so that they can understand each other.

You have two VE.Can ports on the Cerbo GX Mk2.

  1. Connect the Multi RS to one port and terminate both ends.
  2. Connect the BMS cable from the Pylontech to the other port and terminate it. The Pylontech has an internal terminator so you only need to terminate the side on the Cerbo GX Mk2.

In the Cerbo GX you configure what CAN-bus profile you want.

  1. Configure the port connected to the Multi RS as VE.Can & Lynx ION BMS (250 kbit/s).
  2. Configure the port connected to the Pylontech as CAN-bus BMS LV (500 kbit/s)

When correctly configured you can see the Victron devices on one port.

And you can see packets being sent and received on the port that is connected to the Pylontech.

Hey Rhernaus,

Thank you so much for taking the time to explain that to me.

I have reconnected as you said, except I have not terminated the second port in the multi rs. Everything seems to be working fine though!

I have a few errors/warning on the CAN-bus BMS LV (500kbit/s), but I guess it occurred during installation an set-up:

Will keep monitoring to see if it keeps adding more warning/errors…

Thank you,

marco

Nice to hear its working now