Is it possible to use an ET340 ( net meter 3F) and ET112 (Solar meter) meter with a Multi RS 48/6000/100 Solar? The manual mentions VM-3P75CT.

Software is the latest 1.26
This is the first time I’ve used a Multi RS 48/6000/100 Solar with 5 Pylontech US5000s, and the battery won’t discharge.

If I set the net value to -1000 watts in Victron Connect ESS, the battery discharges by 1000 watts, but there is no compensation for consumption.

I see the battery in the device list, and everything seems fine, but with Victron Connect, I see Gel/AGM. Does this need to be set manually, or is it ignored?

Thanks.

It’s not possible to use an ET340 as a net meter with the Multi RS 48/6000/100.
Apparently, only the VM-3P75CT works.
We always used the ET340 with the Multiplus without any problems.

A note that it no longer works with the Multi RS would have been helpful.

The ET112 works fine as an external solar energie meter.