Starting with the basics, and just some food for thought, have you been in and checked that the settings in the MPPT are unchanged and are as they should be.
What is your battery voltage measure device and is this correctly configured to communicate with your MPPT.
What “state” does the MPPT say it’s in if you connect via Victron Connect?
Those panels are correctly wired in parallel, they all have approximately 20V Vmp so wire in parallel. They have massively different Imp so they can not be wired in series.
I answered above, your drawing is the correct connection layout for your panels. Parallel connection needs the same voltage, series connection needs the same current.
Is your charger correctly detecting the system voltage? I.e. 12v system
I’m out on a boat trip all day today without wifi, but if you send as many screenshots as you can hopefully we can spot something out of place that is preventing your system from charging.
after sunrise, the voltage display remains at approx. 11 volts and the system does not produce any power. see screenshot 01
the voltage remains unchanged even after approx. 2 hours of sunlight.
I then disconnected the cables from the panels shortly after 11 a.m. and reconnected them. after that, the system is producing power correctly. see screenshot 01 (I only connected a 120 watt panel temporarily to rule out a source of error).
it should also be noted that the system worked correctly with this setup for almost 2 years. the problem only occurred after the firmware update to version 1.64.
can i possibly upgrade to the old firmware?
I also enclose further screenshots for your perusal.
First off, your system is stating bulk thus it IS charging, thus I don’t think that firmware is your issue.
Also looking at the voltage and current on the input side compared with the output side thay look there or thereabouts thus again in my opinion, the charger is doing as it should and what it can with the input it’s getting.
If I were you I’d be looking for loose connections or high resistance contacts in your PV circuit. As per my last post, are the cables from the panels to the charger big enough to avoid excess volt drop?
It might be worth pulling apart any MC4 connectors you have and checking for water ingress and corrosion?