Smooth peak loads with Victron

From 2027, network charges in Austria will rise sharply. They’re calculated based on kWp (the maximum power drawn over a 15-minute period during the month).

According to my calculations, I’d save around 30% of the total costs if I drew no more than 3 kW from the grid to charge my battery, and used the Victron system to handle peak loads.

What’s the easiest way to do this? Just set the grid setpoint to 3 kW?

Set the input current limit to less than that.

For example:

3000÷230 = 13A. But needing of course a bit of head room - set the current limit to10.5A.

Peak shaving in ess can actually set the two levels. 13A but start shaving for example at 10A.

Set your grid set point to zero unless you need to prevent feedback. That way your solar will cover as much as it can.

Keep in mind this limits the grid connection so selling to the grid is also limited.

This thread might be of interest but keep in mind this uses the same current limit so it has the same flaw.