Charging to 100% only during the scheduled charging stage

Hello,

I have a 3-phase system with 3 x Quattro/15000.

The battery system consists of 14 x Pytes E-Box 48100R units, with a storage capacity of 71 kWh.

In normal operation, the ESS regularly charges the batteries to “only” 94%.
However, if I set a scheduled charging stage with a target of 100%, they are charged to 100%.

Is charging limited to 94% by the ESS or the BMS, or is there something wrong with my settings?
Thanks very much for your help!

Best regards,
Andi

No idea as you haven’t shared these.

Not by ess, possibly by the BMS. You can check with the CCL and CVL
It is also possibly the way the battery detects full.

What are your settings Vs what is recommended by pytes

I have taken the settings from the Victron documents Victron & Pytes at

On this page, the document titled

pytes_victron_ve_configure_setting_with_pytes_48v_batteries.pdf

Does it reach the 53.25v programmed at this point?
You can make a graph on vrm advanced to check soc Vs battery voltage to check

Thank you very much for your support!

At 95%, it was 55.6 V. After I set the planned charge level to 100%, it ran at 100% with 56.3 V.

Ah ok. So the ve configure settings are fallback one

The battery requested charge voltage then needs to be compared to the voltages being reached.