Is temperature taken into account in the LFP charging algorithm (SmartSolar 100/20)?

Hello, first time poster here…

I have a system with:

  • SmartSolar 100/20
  • Battery Monitor BMV 702+Bluetooth
  • LiFePo battery (offgridtec)

The MPPT reads the battery voltage from the BMV Bluetooth “network”.

Now I intend to add a temperature sensor to the BMV and am wondering if it makes sense?

Does the SmartSolar read the temperature? (I think yes)

Does it use the temperature within the LFP algorithm to stop charging below 0 [degC]? This is what I don’t know…

Thankful for any insights! :slightly_smiling_face:

(The battery has its own BMS and should stop charging when the temperature drops under +5 [degC], but I’d like to control this myself. I’m wondering if I need to use the BMV’s relay and the non-inverting VE.Direct cable or if the SmarSolar does it by itself.)

Hi @post.matter, welcome in the blue world

As i know, you must add a extra temperature sensor to the BMV702 for the low temperature shut off

Pay attention to buy the right temperature sensor!

Play a little around with the demo library in victron connect to check out the possibility’s

Thank you.

That helps me only in part :slightly_smiling_face:

If I add the temperature sensor to the BMV and the non-inverting cable between BMV relay and SmartSolar Ve.Direct port, then it will for sure work as intended.

But if the LFP charging algorithm takes the broadcast BMV temperature into consideration, then the non-inverting cable is not necessary.

And if the algorithm takes into the consideration the internal SmartSolar temperature, then no sensor and no cable are necessary!

It just seems obvious to me that the LFP charging algorithm would use the available temperature reading.

The AGM algorithm does this for temperature compensation…

Maybe someone with knowledge of the firmware will read and comment.

Yes, the battery temperature is considered and charging is shut down at 5degC. If there is no external sensor then the MPPT temperature at dawn is used, hence a networked senor is better.

Hopefully your battery BMS has this function anyway.

You could have checked this as noted above by going to the VicttonConnect app and using the demo library ans choosing the SmartSolar 100/20 to see the available settings with a lithium battery.

You don´t need the non-inverting cable between BMV relay and SmartSolar Ve.Direct port if you are using VE.Smart Network with a BMV temperature sensor!
The temperature is distributed via the network and the solar charge controlle switches off by software if activated.

Thank you. You’re absolutely right!

I could swear this option wasn’t available in the VictronConnect App last time I checked… but maybe I oversaw it.

That means the BMV relay remains free for some other application.

(Issue solved!)