Hi, I want to add an extra EM24 to add a 1 phase solar panel to VRM display, is this possible on AC side?. Solar panel is already present on AC in but not visible on overview.
Sure. Just assign it the PV Inverter role in the GX.
You can use a cheaper ET112 for a one phase PV inverter. But then it should be on L1.
You could also use a Shelly meter to avoid a cable (RS485) wiring to the Cerbo.
I need an ethernet meter, ET112 is for 485 connection.
PV is on L3.
Ok, then the EM24 Ethernet Version should be fine.
Main question is how can I be sure the meter will be located in VRM display on AC in side.
You can configure that in the setup, on the GX.
For your existing PV inverter you also selected if it was on AC In or AC Out, right ?
I can not recall being able to select on which side connected, it was automatically on AC out because of using ESS assistant with pv. That’s why I wonder if the 2nd pv will be on AC in.
As far as I know, you can always select on which side a PV inverter is connected.
It’s perfectly possible to run ESS with PV inverter on AC In and/or AC Out side.