PV inverter is shown on AC_Out, instead on AC_Input 1, as configured. No external meter installed.
It is correct on remote console but not on VRM.
Any thoughts are welcome.
PV inverter is shown on AC_Out, instead on AC_Input 1, as configured. No external meter installed.
It is correct on remote console but not on VRM.
Any thoughts are welcome.
sometimes this change takes a little while to update.
Thank you for reply.
It is like so since first install, no change after 3 days, Venus OS 3.67
Without external meter you can’t have PV on the AC input.
Thank you !
After a new reading of ESS instructions and re-view the logic, this is my conclusion as well.
This small system, Dyness 14kW battery and Multiplus II GX 5000, is used solely as a UPS.
I was hoping to not need a Smartmeter as install position is quite far, but still benefit of installed Fronius PV. Ethernet is also not easily available in the main power distribution area.
From your experience, do I have other option other than: