PV show wrong on AC-Out

PV inverter is shown on AC_Out, instead on AC_Input 1, as configured. No external meter installed.

It is correct on remote console but not on VRM.

Any thoughts are welcome.

sometimes this change takes a little while to update.

Thank you for reply.

It is like so since first install, no change after 3 days, Venus OS 3.67

Without external meter you can’t have PV on the AC input.

Thank you !

After a new reading of ESS instructions and re-view the logic, this is my conclusion as well.

This small system, Dyness 14kW battery and Multiplus II GX 5000, is used solely as a UPS.

I was hoping to not need a Smartmeter as install position is quite far, but still benefit of installed Fronius PV. Ethernet is also not easily available in the main power distribution area.

From your experience, do I have other option other than:

  • drop the ESS and have a “dumb“ UPS system, PV unaware ?
  • or
  • do the reasonable it takes for a Smartmeter install ?