I’m adding a second array and Charge Controller to my existing system which has these connections…
A VE direct connection between the Venus GX and the SmartSolar MPPT VE.Can 250/100 Charge Controller.
A VE Can connection from the Venus GX goes to the Quatro inverter.
A VE Bus connection from the Venus GX goes to the Pylontech batteries.
What connections do I need to add the second VE.Can 250/100.
VE CAN → doesn’t connect to the Quattro. It only has one VE.Bus port.
VE Bus to Pylontech → that can’t be right either. Pylontech only has an RS485 or CAN port.
Unfortunately, the Venus GX only has one CAN port (which is occupied by the battery). So you can’t connect the two charge controllers via CAN. You can only use the second ve.direct port and connect the second charge controller there with a suitable cable. If you absolutely want to use CAN for the charge controllers, you’ll need to upgrade to a Cerbo. It has two independent CAN ports.
VE.can is a bus. You can daisy-chain multiple devices with a terminator on the device at each end of the bus.
The GX supports two independent CAN busses. The VE.can MPPTs have two CAN ports - they simply pass the bus through so it can be extended to another VE.can device.
For the MPPTs, GX gets a terminator and a cable plugged into the 2 VE.can 8P8C (“RJ45”, sic) ports. That cable goes to first MPPT, which has another cable going to the 2nd MPPT. That one also gets a terminator.
Cable from GX VE.bus port to the Quattro.
You should be able to connect to the battery using the other, CAN-2, bus on the GX, but you have to wire to it. It doesn’t have 8P8C ports, it has a terminal block. You’d cable it with a 120 ohm termination resistor between CAN-H and CAN-L. The other end goes to the battery, which also gets a terminator.
Thanks Jens, you’re absolutely right, whilst tracing the wires through crowded conduit I must have got my wires crossed, literally.
So yes it is, VE.Can to Batteries and VE.Bus to Inverter. The charge controller is connected using VE.Direct. My thought is to connect the 2nd Charge Controller with another VE.Direct cable. Is this the best way to do it.