Hi Have just performed a remote update to my inverter.
The update went through successfully. However the inverter did not start up.
Only when I disconnected the VE-BUS cable to the Cerbo did it start up.
I the used the remote config to reconfigure the system - and again update went through -but inverter did not restart.
When I unplugged cable inverter came back on.
Apply a production version of the GX, you never know if the beta is complicating the issue. Check that the GX doesn’t for some reason have the inverter software switch set to off.
Thanks for that, I couldn’t find those detail anywhere…
Still, there doesn’t seem to be a good reason for me to upgrade to v555, on the principle that there are always risks with doing this and you should only do it if there’s a good reason for doing it – which there was for v552 to get solar/wind priority working.
If this changes in the future then I’ll reconsider whether to upgrade or not.
still not connecting on generator “solo”, still need 1.5kw load on generator, running without the frequency is constantly shifting between 60.7 and 61.8Hz, Multiplus is hunting, but the hound never gets the hare.
Strangely enough, when i set the MP to “charge only” it will show me an AC-Out frequency, and will try to synchronise. Every other charger in the world would work on any frequency, stable or not…
The generator is a 6.5 KW Onan LPG, 16.000€, 20 years old.
Yes, i have to, my generator is 60hz, grid is 50, as is the native frequency of my multiplus.
But my mechanical generator is shifting frequency faster then the electronics of the MP is willing to follow.
I would have programmed the system so that it just takes over the frequency/phase from AC-in as setpoints instead of trying to synchronize. But ofc I’m only an engineer with 50+ years experience
Ok, victron and i seem to have different opinions how a “ups” function works, without this the MP synchronizes with the generator, even without connecting a resistive load.
But the batteries are still being charged with 100 of the possible 120a.
HI Johan,
Looks like your thread has been hijacked… IN regards to your question about Inverter not starting. This is not a new issue due to the upgrade. I have systems that have the same problem with older version I have never received a good explanation.
My Experience is primarily with Quattro products. We do not use many multiplus.
Problem is particularly accute if you have the Inverter in “remote OFF” or “Charge Only” with loss of DC power. The system gets locked into an OFF state and the only way to recover is to unplug the Cerbo. then miraculously after a few seconds the Inverter or charger If AC is present restarts. Switching the Quattro ON/OFF does not restarts the system as you would hope it does. It “appears” that the Cerbo is the one holding the system OFF.
This is a particularly annoying “feature”. Here is link to the post i Wrote:Quattro VeBus Loosing Connection after remote Charge Only mode - #7 by Jean-Marc
Using the Cerbo to switch between state if the Quattro is listed does not produce any change. Sometimes after a Cerbo reboot, the Quattro does not reappear in the device list. So the Quattro seems physically OFF.
Sometimes I have to both remove the Cerbo and cycle the DC power for the system to work.
Im Online Handbuch wird unter FAQ 19.2.20 dieses Problem behandelt. Das Problem tritt in der Regel dann auf, wenn der Cerbo nicht aus der Batterie versorgt wird oder die Batteriespannug nicht mehr zur Stromversorung des Cerbo ausreicht. Der Multi/Quattro wird durch den Cebro verriegelt und kann solange der Cerbo nicht wieder läuft nicht starten.
I found the same problem with a Multiplus 48/3000/35-16 (brand new older model) and a CCGX. I updated everything to the latest production versions (as at 8 March 2025 - not Beta versions), but when I installed it (on a remote off grid site without internet), I had to unplug the VE.bus cable to get the Multiplus to start.
The settings I used:
Other grid code with wide input frequency and voltage ranges
Shut down on SOC enabled
Lithium battery
No VS
No assistants
I need a solution. I cannot expect my customer to disconnect cables to switch the system on.