Hello everyone,
I wanted to share my situation to see if anyone can help me with the problem, or whether it could be a fault with the inverter.
I currently have an off-grid system consisting of the following components:
Solar panels
Victron MPPT 150 85 -tr
Victron Energy Multiplus 24 5000 120
Turbo Energy Lithium Series 24V 2.24kWh battery
*As a note, until 2 years ago, there were lead-acid batteries connected in series, but these were replaced with a lithium one, which is the one listed above. I think the inverter and MPPT settings were never changed.
Right, the problem is that the inverter did not cause any problems until 2 months ago, but we have now noticed that when it has normally been running for 3 or 4 hours, the overload LED on the inverter comes on. After that, sometimes the low-battery warning comes on as a result of these faults.
What I did was update the inverter to the latest version (2614556), and update the charge and generator settings to the values specified by the battery manufacturer.
After several days of testing, I think it now lasts a little longer, but eventually the overload still comes on. Another test we carried out when it starts to fail is to disconnect the entire domestic network by removing the OUT cables directly from the inverter so that it cannot supply any kind of power, but the overload still comes on.
I have also noticed that, before the overload LED comes on, the inverter starts making a strange noise.
The MPPT is almost always in FLOAT, and when I set it to Charge only, none of the LEDs on the left-hand panel comes on. I seem to remember that they used to before.
Finally, I should add that the battery is always at 100%. On some occasions when the inverter trips, the alarm LED on the battery also comes on until you restart everything, at which point it switches off.
The photos were taken with the equipment switched off.
Could this mean that the inverter is knackered, or is it a programming issue?
I would be very grateful for any help you can give me.
Kind regards!!