ESS Setup with Cerbo GX and Solaredge and Fronius Inverters

On the next weekend my electrician and me we will install a 3-Phase ESS with Victron Multiplus II, Cerbo GX and Pytes batteries. I am still running two PV installations. One with a Solaredge (SE10k) inverter and one with a Fronius Primo 4.6 inverter.
My Question is, is there a way to run both inverters behind AC out (AC Coupled)?
I know the documentation from Victron for both vendors. And I recognized the different frequency settings.
Has anyone experience with such a mixed setup and some hints or maybe a solution for me?

Thanks
Sebastian

Do remember that the 1:1 rule applies.
You should be able to program the P(f) curve of both inverters so that proper limiting applies when the mains is disconnected.

1 Like

Sounds tricky but you can set same frequency derating on both inverter. On the Fronius just to into expert menu, touching the third button 5 times and introduce code 77634. There you will find the option to modify the frequency and derating factor, just set the same as the solaregde, that should work :flexed_biceps:

1 Like

Thanks for your hints @MikeD and @Solarmaxcanarias.
I will try to set change the frequencies to the same value.
I know the 1:1 rule and comply with it.
Commissioning was planned today, but the electrician did not have time at short notice. So I have to wait to try out your hints.
I will let you know if it works in the next weeks.

@Solarmaxcanarias I tried to find the correct settings in the expert menu. But there are quiet a lot of settings and I am not able to compare the Solaredge settings to the Fronius settings.
The Hz values are also different to the Vicrton manual ac_coupling_fronius
Can you tell me the right point in the expert menu for Start, Minimum and Disconnect freq?
Thanks so far
Sebastian