Yes, the 1:1 rule means that I can’t have more than 45kva Fronius AC coupling input into my system.
that will be achieved through limiting the total of the Fronius inverter capacities.
I have to undertake more research to see how to parallel multiple Fronius inverters and whether, as with Victron inverters, they need to be identical models?
The 1:1 rule also relates to battery capacity, the victron system has to be able to absorb all energy from the fronius inverters when for example a load gets turned off.