Hello,
I came across 2 fronius symo 12.5 3 phase basically free, i have 30 kwp panels that the fronius will connect to.
Can 2 fronius ac couple with my 3x 48/15000kva multiplus ii off grid victron and use the microgrid frequency shifting?
Thanks!
Hello,
I came across 2 fronius symo 12.5 3 phase basically free, i have 30 kwp panels that the fronius will connect to.
Can 2 fronius ac couple with my 3x 48/15000kva multiplus ii off grid victron and use the microgrid frequency shifting?
Thanks!
@offgrideu
Yes.
And you already are observing the 1:1 rules.
Yes you and i already discussed that, thank you for all the support!
Please also note the minimum requirements for the battery size with regard to the factor 1 rule
Thank you, yes that was discussed in a seperate post.
Will the cerbo see both inverters? Or treat them as one? (for vrm monitoring display and logging purposes)
The cerbo will show both inverters individually as two devices, you can create custom dashboard-graphs etc.
However, on the Dashboard there is only “One” PV-Inverter tile (One on the AC-IN side, one on the AC-out side), that will always be the sum of all connected PV - Inverters on the respective side.