Hello

I would like add a VICTRON multiplus ii to my system in order to have backup power. Actually I have 10 x 455W solar panels in South orientation with a Fronius Primo 4.6 and 2 x 550W solar panels in west orientation with a APSystems DS3-H 960W.

According with technical spec inverter and micro iverter support AC coupling but I don´t know if the Frequency Shifting mode works only with the fronius and the DS3-H whit frecuecy increment shut off, or both works well Frequency Shifting mode or the Frequency Shifting mode not work with 2 diferent inverter

My total solar power are 5560W ( I will never achive due panels orientation) I comply the 1:1 rule?

What battery capacity do I need?

Thanks for your atention

Regards

easiest way to do this would be to wire the fronius inverter on the AC out, and the micro inverters on the AC in. That way, you need only a 5kW inverter, not a 10kW(6kW as 2x3kW in parallel) to comply with the 1:1 rule.
Battery sizing depends on the inverter voltage (typ 48 - 52V) and the battery type. More information on that can be found at : Battery Compatibility [Victron Energy]