My situation is this:
EasySolar 48/3000, fw 556, grid meter
ESS is installed and configured for “optimized (without batterylife)”
Grid setpoint set to 50W
Feed-in disabled
What I am seeing is the grid being used to supplement solar to power loads during the day.
Is it possible to configure ESS to prioritise battery over grid at all times?
ah ok, if the Loads are above ~3000W, doesn’t the multiplus power assist?
so for say a 4kW load, the multiplus will be in inverter mode supplying 3kW and then 1kW comes from the grid (assuming solar is zero)?