I’ve had an ESS with a MultiPlus II and a DIY battery with a REC BMS since around December last year.
It worked perfectly for many months. However, for some time now, it keeps happening that the ESS doesn’t charge even though there’s enough surplus PV power available. The next day, it may work perfectly again. Restarting my Ekrano has no effect. If I restart the BMS, it works again. I’ve also already received an update for the BMS from REC. It then worked normally for a few days, but the problems returned, although they seem to occur slightly less often.
Are there any ways to debug this? For example, can I see somewhere whether the BMS is limiting the charging current?
A few relevant settings:
ESS Optimised without Battery Life
Scheduled charging levels inactive
DVCC, STS and charge-current limitation enabled
REC BMS detected correctly and active as the controlling BMS
So, does that mean you’re measuring the PV output separately and that the GX also “knows” about it? In other words, a PV meter on “AC In”?
The system will only use the power to charge the battery if it detects that you’re generating PV power. Simply displaying surplus on the Grid Meter doesn’t mean that the system is charging from the surplus.
You can also go back in the VRM overview to compare the data … and how did your system reach 80% SOC the previous day?
Quite right, the voltage issue should have stood out.
Here are the last two days; yesterday was fine. So the settings should be correct too—I’d already sent them to REC before. In any case, I’m now seeing exactly what I wanted. I’ll send the screenshot to REC Support.
What do you mean? When it’s running, it looks good. But I still don’t have an explanation for why the BMS lowers CVL at 50% SoC, and does so irregularly.
The VE Configure part would only be interesting because the Multi acts as a charger … but as you can see, your BMS lowers the charging voltage and sets the current completely to 0 even though the SOC isn’t 100% … do you have temperature sensors on the BMS that could be responsible for this? …
Temperatures are usually between 30 and 35 degrees. It doesn’t correlate with the behaviour, and there’s no alarm showing on the BMS either—nothing in the logs, either.