Hello,
My supplier provides 3x230V 25A (I had 3X230V 20A until a few months ago).
So I’m used to watching my consumption ![]()
I’ve thought of another option:
A single MP 48/6K5/100-50, configured for single phase between L1 and L2
AC IN: 25A (limited by the supplier)
AC OUT: 45A (25A from the grid + 20A from the battery)
The MPPT –> max. 190A DC at 48V (with no feed-in to the grid)
The batteries –> 200A BMS x2 (or x3 if I add another one), 17kVA per battery.
If demand is below 20A AC… I don’t discharge the batteries (unless the charge level is below 50%).
If demand is between 20A and 45A AC… I discharge the batteries and draw power from the grid
If the grid goes down, I’ll be limited to 20A AC… that’s fine
Demand between 20A AC and 45A AC is rare
My thinking: a 45A single-phase installation is more or less equivalent to 3x230V 25A in delta.
Managing consumption:
What do you think?
If you have a three-phase supply without a neutral and use three-phase appliances (even ones that don’t need a neutral), such as a hob, it’s impossible to run them with a Victron system because a neutral is required.
If your three-phase appliances that don’t need a neutral can be wired to run on single phase, then you’ll need to modify your installation to single phase before fitting Victron inverters.
If you absolutely want to keep your three-phase appliances and still install Victron equipment, the only solution is to fit a transformer at the grid connection to your home. It’s expensive, noisy and emits magnetic fields; what’s more, the whole installation and the consumer units will need to be replaced.
Another option is to split your installation into two parts, leaving out the three-phase appliances and managing only the single-phase ones. The consumer unit connections will also need to be modified.
PS In all cases, also be wary of connecting any existing AC solar inverters to your installation, as they’ll impose additional constraints. I can still give you a call if you leave me your number.
Before considering anything, be sure to define your objective: do you want energy storage that remains connected to the grid, or total or partial off-grid operation? In the first case (temporary storage), it will always work with three-phase power without a neutral.
@ Bertrand
That’s definitely a good option, but there are some unknowns in the scenario, particularly how you’re charging the batteries… There are technical constraints too: what’s the maximum current required on AC OUT?
None of my loads are three-phase, as my cooker doesn’t support a delta connection.
And indeed, this means switching the installation to single-phase, which will be easy because I have 3 distribution boards, all wired for single-phase. (Board 1 on L1L2 with 300 mA protection, board 2 on L2L3 with 30 mA protection, and board 3 on L1L3 in the attic for the lights, with 30 mA protection.)
And if 45 A isn’t enough, a second MultiPlus connected in parallel could provide an extra 20 A during peak demand.
As I’m single, my consumption is low: one load of washing per week and one dishwasher load per week. There’s no need to run them at the same time.
All my circuit breakers for the loads are either 6 A (lighting points) or 16 A (sockets), except for the cooker, which is on a 25 A breaker.
The batteries will be charged mainly by the 10 kWp solar system, which will only charge the batteries (no feed-in to the grid).
And 25 A from AC-IN when I’m not using power; I’ll have to set the operating schedules correctly.
As all my loads (on relays) and lighting points are controlled by home automation, I could manage the loads according to the battery charge.
Check this out.
It does work.
@Q.x @Ludo_CC @Eric @bertrand
Check this out.
3x230 covered in full.
MultiPlus-II GX in 3x230V network, integrated / controlled with Arduino ESP32 - Modifications - Victron Community
Hello Bertrand,
How are you getting on with your project? I want to do exactly the same MultiPlus II installation on L1 & L2 (from a 230 V three-phase supply with no neutral).
Have you managed to resolve this neutral test issue?
Thanks
Hello everyone,
I’ve just had my installation commissioned and came across this thread because I’m also experiencing the problem of VRM AC loads being too high on a 3x230 V system without a neutral. So I thought I’d share what I’ve found:
My installation:
Cause:
The problem is with Venus OS: it calculates consumption phase by phase and clamps each negative phase to 0 (see dbus-systemcalc-py/dbus_systemcalc.py at 7694578f610bc301223a4120c39059abf3f916dc · victronenergy/dbus-systemcalc-py · GitHub).
The result: L1 = 190 + 340 = 530 W, while L2 = 0 instead of −125 W, so VRM shows 530 W of loads even though the actual balance (PV − battery + grid) is about 405 W. The overestimation is constant—about 3 kWh per day in my case.
As far as I know, there’s no setting to correct this. It doesn’t affect how the system operates, since ESS regulates based on the total, but the consumption display and VRM forecasts are inaccurate. This could matter if you use Dynamic ESS.
To get an accurate consumption figure, you have to calculate it elsewhere: PV + net grid − battery. I do this in Home Assistant via Modbus TCP.
Hello,
How did you solve the ground relay test problem on startup?
When you select the network code, the test box turns grey.
Thanks
Hi Thib, the best thing to do is contact me:bertrand@duvivier.com