Hello everyone,
I am planning a three-phase Victron ESS and would like to clarify whether it can be implemented with only one AC cable each to the MultiPluses.
Components:
3× MultiPlus-II 48/6k5
NKON ESS Pro 32.15 kWh
SMA Sunny Tripower X 20, 24.94 kWp PV
Sunny Home Manager 2.0
Cerbo GX
TN-C-S system; PEN split into PE and N in the main low-voltage switchboard (NSHV)
The MultiPluses and the battery are to be installed in the garage. The Sunny Tripower is located in the house, in the attic.
Unfortunately, there is currently only one cable between the main low-voltage switchboard and the garage:
NSHV → boiler room → garage: 5×16 mm² Total length approx. 45 m
plus 4× Cat 7 and 2× J-Y(St)Y 4×2×0.8
OS2 single-mode fibre-optic cable in future
The garden has only just been reinstated, and of course the conduits were chosen too small—don’t ask…
Main question
Can the existing 5×16 mm² cable be used in grid-connected operation as the connection to the garage and, after suitable all-pole grid isolation, as an AC-out connection back to the NSHV or the entire house network?
I am thinking of an “External Transfer Switch Application” with the grid disconnected in the NSHV.
This raises the following questions:
Is there another Victron-supported topology in which the 5×16 mm² cable can be used in both grid-connected and backup-power operation?
In the “External Transfer Switch Application”, can an EM540 replace the voltage path directly connected to the MultiPlus (AC IN) and the connected current transformers, or is it suitable exclusively as a grid meter for normal ESS control? Can its voltage measurements also be used, or are the separate AC-IN voltage-sensing cables to the MultiPluses still essential?
Ziehl UFR1001E and Sunny Tripower
The Victron Anti-Islanding Box with the Ziehl UFR1001E caught my eye. As I understand it, the Ziehl takes care of external grid and system protection and controls or monitors the grid-isolation contactors.
The Sunny Tripower X also has:
DI6 for external grid and system protection or rapid shutdown
DI1–DI4 for external active-power setpoints
Would the following sequence be technically possible and, if applicable, even approved by Victron and SMA?
The Ziehl detects the failure of the public grid.
The grid-isolation contactors open all poles.
At the same time, the Sunny is initially stopped via DI6.
The MultiPluses establish the three-phase island grid.
The Sunny is enabled again.
In island operation, a maximum active power of approximately 10 kW is continuously specified via DI1–DI4.
The P(f) control then takes over ongoing power adjustment.
Would this work, or am I missing something?
For now, I am looking for a fundamentally functional and officially supported topology that does not require installing a second power or voltage-sensing cable between the house and the garage. This concept will then be discussed with the electrician working on the house and property.
Thank you very much for your help.