Compatibility of Quattro with Quattro ii in three phase setup

Just wanted to ask i anyone could provide me with the compatibility ID of a newly shipped Quattro ii 48V 5000VA 70A 50/50 230V?

I am currently running 3 Quattros 48/5000/70 100/100 230V in three phase setup. This devices have comp ID 2658 and i am facing a little bit of confusion with my supplier about the question: If one of these quattro would fail, could it be replaced by a quattro ii 48/5000/70 50/50 230V ?

As for my understanding the comp ID must be identicaly for any ve.bus system. The letter at the end would only come to play if i would have parallel devices in one phase - what i don“t have.

Am I correct so far and what would be the comp ID of the Quattro ii mentioned?
Greetings to everyone and thanks in advance for all help.

The old Quattro can’t be used together with the Quattro-II.
Not in 3-phase and not in parallel.

The Quattro-II 48/5000/70-2x50 is 2651.

Thanks so much for the fast reply and clear help! I feard exatly that but my supplier said: ā€œno it would be just fineā€
You helped me a lot thank you.