Hello everyone,
we are the happy owners of a three-phase system with three MultiPlus 3000 units, two MPPTs and a Fronius Primo on AC-Out. Three Pylontech US5000 batteries are charged by the system.
The system is currently configured off-grid and provides hot water and supplies selected circuits in the house — there is no grid connection whatsoever.
Nevertheless, we would like to convert it to a grid-connected setup, as there can be significant excess energy in summer, while things can occasionally become tight in winter. I have now come across the requirements under §14a and §9 EEG. An EM24 is installed between the grid feed-in point and the house distribution board. In other words, the EM24 can also measure other household loads on the grid side.
§14a — in other words, switching off the charger — works perfectly. The control line is connected to AUX2, and grid charging can no longer take place. So far, so good.
The tests for the §9 EEG configuration have not been quite as encouraging so far. When AUX1 is switched, no more energy is fed into the grid, thereby complying with the statutory requirements. However, loads connected on the AC-In side are NO LONGER supplied by the PV system at all, because not only the feed-in power to the grid is switched off, but also the power within the house. Only loads on AC-Out continue to be supplied, provided that PV output and battery SOC allow it.
At least the Fronius, which is connected via Modbus/TCP, is controlled accordingly.
In short: at least as far as the grid operator is concerned, this is compliant, and the feed-in can be reliably switched off using an RSE or control box. Unfortunately, this also affects the loads on AC-In — the benefit of now being able to supply these via a grid-connected setup would disappear in the event of throttling or shutdown, and only AC-Out loads would continue to be supplied.
If we switch the ESS to zero feed-in, that also works perfectly and the grid power is quickly regulated to 0 watts. Here too, however: when AUX1 is switched, all consumers on the AC-In side are then supplied only by grid power.
Is there any setting that makes “Disable-Feed-In” mean only “actual feed-in”? Or is a new update planned for this in the near future? Or will I have no choice but to connect the entire house to AC-Out?