nicola-marrati avatar image
nicola-marrati asked
MPPT 75/15 SMARTSOLAR DOESN'T SWITCH TO FLAT WHEN THE BATTERY IS FULLY CHARGED
Hallo to everyone.
I have a 100w solar panel and two 320A batteries connected with MPPT 75/15 smart solar charger.
The question is : why the charger dosen't switch to float program when the batteries are fully charged ?(I suppose 13,8V the charger could be to float charging as show in the pictures)
I alwais see bulk charging during the day, none absorbition and float switch
Nothing happens also if I turn off the load.
Where is the problem ?
Thank you for every suggestions
I post the MPPT settings and the initial app screen
MPPT SmartSolar
pwfarnell avatar image
pwfarnell answered ·
How discharged are the batteries, how many Ah needs to be replaced. 100W of solar panels is quite small if you are discharging the batteries a lot and will really take a long time to recharge. If you have discharged your batteries by 25% then you need to recharge 160Ah, which will take 43 hours at 3.7A. 100W of panels is really a trickle charge for 640Ah of batteries, it might never be able to get to 14.7V.
As a comparison, on my boat in the UK I have 690Ah of 12V AGM batteries and 680W of panels. I could manage with less solar in the summer, but 100W would be too small.
Can you also make a screenshot of the history?
The MPPT only switches from bulk to float after the absorption voltage is reached, in your case 14,7V.