question

Javier Moran avatar image

Limit Discharge

Dear Community, good afternoon


Currently working in setup with an EasySolar.

I will configure it as "Keep batteries charged". This way when batteries are fully charged any PV power will be used by the loads.

In case of grid failure I would like to discharge the batteries to a certain limit and then shut the system down until grid power or solar power is available again to recharge the batteries. Is this possible?.


Thanks for your help.

Best regards,

ESS
1 comment
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

I deleted my previous answer because it was wrong. I misunderstood.

1 Answer
nickdb avatar image
nickdb answered ·

You can set inverter shutdown and restart soc limits in the config tool.

2 comments
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Dear nickdb, good afternoon


Thanks for your quick answer.

So there will be no conflict between ESS and this limit?

Thanks for your attention,


Best regards,

Confirmed. There is no conflict. In fact when you setup ESS, it asks you to specify 4 Dynamic Cutoff values based on different loads.