peterh asked
Inverter goes to 'passthrough' as soon as contribution from PV/MPPT's drops below AC Load
My system is a new system based on two Multiplus II 3000/48 connected in master/slave, two 150/45 MPPT's, CCGX, and a BlueNova battery connected via Canbus.
I have the latest firmware installed on the MPPT's, Multi's, and CCGX.
When the system is physically disconnectted from the grid it is functioning perfectly supplying the critical loads and charging the battery during the day and running off battery at night.
I'm currently trying to implement ESS.
During the day when the contribution from the MPPT's exceeds the AC critical load it functions as expected in charging the batteries and supplying the critical loads.I have set the grid setpoint to -20W to always have a slight export to the grid.
However as soon as it starts getting dark the inverter switches to passthrough mode and supplies the load from the grid even though the battery SOC exceeds 98%.
Are there any other settings on the CCGX or the Multi's that I am missing?
ESS
Rob Duthie avatar image
Rob Duthie answered ·
Hi
With lithium batteries turn off the mode for battery life to off without as this makes big difference how the ESS system works only designed for lead acid.
Had a a similar issue.
Regards
Rob D
NZ
peterh avatar image peterh commented ·
Rob,
I can't see that it's possible to disable the BatteryLife option
Now I understand what you mean - and have switched off
Hi @PeterH
I'd check the options at Q9 of the ESS faq first:
https://www.victronenergy.com/live/ess:design-installation-manual#faq
9 comments
Daniel,
Have checked everything on the list and can find no issues.
have also disabled the BatteryLife option and reduced the battery voltage limits.
The chart below shows what is happening.
During the day run off the solar only.
As the sun sets there is a brief period where there is a contribution from grid, solar, and battery.
Then goes onto passthrough and runs off grid only.
The following morning effectively transfers back to solar.
Until I can resolve this problem am every night now switching off the supply to the inverters (grid failure), and running the whole night off the battery.
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ peterh commented ·
Hi @PeterH
What is your VRM id? I can take a look if you want.
peterh avatar image peterh Daniël Boekel (Victron Energy Staff) ♦♦ commented ·
Daniel,
Don't want to post this on the forum. Let me have your email address and I can give you access.
Peter
Hi @PeterH
You don't have to post publicly, you can select who can see it by clicking on 'Viewable by' below the text box.
Also please don't add me through email, just the VRM id / name is enough for me to look into it.
jonjex avatar image jonjex Daniël Boekel (Victron Energy Staff) ♦♦ commented ·
Hi Daniel, Did you have a chance to look at our issue
jonjex avatar image jonjex jonjex commented ·
@Daniël Boekel (Victron Energy Staff) have you been able to have developer look into this ?
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ jonjex commented ·
Hi @jonjex
I see that since a couple of days the system seems to be working correctly again? did you change something to get it like this?
Yes. It was an issue with the inverter. Once that was replaced system worked fine
Hi @jonjex
We've not found anything yet.
did you already try to reset the Quattro? (turning it off and on again does the same)
I've asked another person to look at it today, with a different specialty.