question

kickus avatar image
kickus asked

VE.Can SmartSolar not showing up in Cerbo GX

Hi,

I have a new setup which is failing to establish VE.Can communication with Cerbo GX and SmartSolar MPPT 250/100 MC4 VE.Can. The solar chargers are neither visible on VRM or in Cerbo GX console.

I want DVCC in use, in order to scale up with additional solar chargers while having a system-wide max charging current defined.

Please help - I'm running out of ideas. How can I get the Can devices visible? I have terminated the Can bus in both ends.


Br,

Kristian

1720443181361.png1720443157098.png1720443200216.png

1720442610570.png

1720443329284.png

1720442634473.png

1720442737742.png

1720442811993.png1720442837889.png


cerbo gxMPPT SmartSolarVE.Can
1720442610570.png (366.7 KiB)
1720442634473.png (236.4 KiB)
1720442737742.png (362.1 KiB)
1720442811993.png (168.5 KiB)
1720442837889.png (353.9 KiB)
1720443157098.png (3.9 MiB)
1720443181361.png (4.0 MiB)
1720443200216.png (3.1 MiB)
1720443329284.png (320.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @kickus

The cable you are using between the MPPT and GX device is a special and specific cable that is intended only for BMS-Can devices.

Replace it with a regular RJ45 CAT5e or CAT6 networking cable and it should work as expected.

You can tell by those white text labels at the ends.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kickus avatar image kickus commented ·
Big thanks, that explains it! I’ll replace them and will accept the answer once I’ve confirmed the success.
0 Likes 0 ·
kickus avatar image
kickus answered ·

Thanks a lot, your advice solved my problem. I had missed that it was a non-standard ethernet cable, I had accidentally ordered them as VE.Can cables. Now my SmartSolar charge controllers are showing up in VRM as expected. 1720699625948.png


1720699625948.png (126.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.