Ess minimum soc ignored?
Multiplus 2/5000 with 25khw of pylontech. Using ess I set min soc @ 40%. This works fine. Occasionally, I want to discharge more deeply, eg, because my wholesale tarrif is unusually high and I am prepared to risk running out in the event of an outage.
But I've found that setting min soc to 30 for example is ignored, and I am drawing from the grid, with the battery sitting at 40%.
Is there some other limit I need to check?
Thanks
Russell
(venus 2.90)
ESS
@Russ
Could be active SOC if you are using battery life. Confirm nothing else is showing like sustain?
russ avatar image
russ answered ·
Ok, sorted.
I found I had a 40% soc set in veconfig.
Must have been leftover from my previous agm battery.
I also updated the ess assistant and venus to 3.33
Now down to 30 as set. 49.1v
Thanks for the pointers.
Duivert NL avatar image
Duivert NL answered ·
is battery life on? this can prevent a lower SOC
russ avatar image
russ answered ·
Battery life not on. No other indicators, except for a low battery alarm at 48.75 (I see previous alarms at various voltages, 48.42, 48. 94 etc. But they don't seem to align with the 40% limits.)
@Russ
Maybe voltage drop under load then.
With ESS what are your dynamic cut off voltages?
Is the pylon set as the system battery monitor?
lifeingalicia avatar image
lifeingalicia answered ·
If you have low bat alarms before 40% check if bats are balanced it would be logical for the system to ignore SOC if low bat alarm. VE settings? 48.75 would be around 15% SOC...