mr-manuel avatar image
mr-manuel asked
RCD tripping when connecting to grid after firmware update
after I updated the firmware of my MultiPlus II 48/5000/70-50 from 497 to 508 every time I try to connect the grid the RCD trips. If I put the MultiPlus in "Charge only" then it works without problems.
I live in Italy and have this constellation:
Grid -> RCD 30mA (which trips) -> MutliPlus II -> RCD 30mA -> Mains.
When I bypass the MultiPlus II by cabeling all works also fine. Before the firmware upgrade everything also worked fine. I checked everything on cabeling, but it makes no sense to me, since nothing changed and it is working when I put the MultiPlus in "Charge only".
To me it seems, that the grid relay is not disconnecting before connecting the grid, but I don't know why.
Is there a way to downgrade the firmware to 497 again? Unfortunately I was not able to find the firmware on professionals.victronenergy.com, a direct link would be great in case I missed it.
rcd trippinggrid relay
nickdb avatar image
nickdb answered ·
I think you need to return it for bench testing. If you have followed the advice here for error 11 and the firmware is current, which it seems to be:
https://www.victronenergy.com/live/ve.bus:ve.bus_error_codes#:~:text=Error%2011%20indicates%20a%20failed,failure%20(eg%20inoperable%20relays).
Then, most likely, one of the dual input relays has failed.
Alex Pescaru avatar image
Alex Pescaru answered ·
mr-manuel answered ·
Ok, now I downgraded the firmware, but the error persists.
I now replaced the RCD with a normal braker and now I get this error:
mr-manuel avatar image mr-manuel commented ·
After the change of the relays all is working normal again.
dansonamission avatar image
dansonamission answered ·
We just updated the same unit from 498 to 510 and rcd now keeps tripping. This is a new unit. Doesn't matter which mode its in, inverter or charger.
If you know, what you are doing then connect the MultiPlus directly to the power source without RCD (but with a normal braker to protect the cables!) for the time of testing only and see, if then you get an error message in the GUI/remote console.
If you are no electrician then bring the device to a Victron partner nearby and let them check it for you.
giampaolo avatar image
giampaolo answered ·
Hi mr. Manuel I have seen that you are in Italy (the VE Bus screen shows Italy CEI 0 21). Since I am in Italy too, my I ask you wath kind of external IP interface protection are you using . Regarding your problem with the RCD I have seen in many installations that is used a 300mA device on the inverter line.
Yes, I have also a 300mA one between the grid connection and the AC-In of the MultiPlus. But in my case the problem was a faulty ground relay.
daza avatar image
daza answered ·
I’d say use a 100ma time delay rcd on it which would allow your RCBO’s to trip before the multiplus, I’ve got one on mine being a TT system not had it blip at all. Hope that helps