SmartMPPT 150/60 always floats unless pull Remote on/off terminals.

SmartMPPT 150/60 always floats unless pull Remote on/off terminals.


when the jumper is in it shows 13.5 v no matter what pull it out reads voltage correctly goes to bulk thnn stops to float again

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

11 Answers
snoobler avatar image
snoobler answered ·


1696896988091.png

Fine here, but the inverter battery monitor can't see anything the MPPT sends in, but it will get overridden by the shunt value if the shunt is the default battery monitor.


1696897002129.png

Would raise shut-down to 12V and change the restart and pre-alarm to 12.8V. Powerassist is enabled.


1696897014722.png

Looks good.


1696897031171.png

Looks like you have an assistant that turns on ACout 2 when SoC is above 61% and off when below 60%.

Under settings > VRM online portal > VRM two way communication must be enabled.

Also worth setting the logging interval to 1m when trying to troubleshoot issues.


1696896988091.png (74.6 KiB)
1696897002129.png (53.1 KiB)
1696897014722.png (42.3 KiB)
1696897031171.png (15.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

Snapshot of charger settings, including expert?

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

s1277 avatar image s1277 commented ·

img-3763.pngImage Caption

img-3758.png

img-3759.png

img-3760.png

0 Likes 0 ·
img-3763.png (76.5 KiB)
img-3758.png (195.6 KiB)
img-3759.png (192.5 KiB)
img-3762.png (77.3 KiB)
img-3761.png (83.8 KiB)
yotamota avatar image yotamota s1277 commented ·
haha I didn't know you were on here to snoobler!
0 Likes 0 ·
rausimous avatar image
rausimous answered ·

bulk means that your mppt is limiting the current to your batery either because of low solar input or because of maximum current (in your case 60A)

when your solar panels only deliver 135 w your charger will put all 135w in your battery (13.5v 10A) in bulk mode

float is when your battery only accepts 8A (anyting below 60A and below the solar aray output ) at 13.5v (float means that your battery is limiting the maximum charge current [to full to charge]

so float is normal

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

s1277 avatar image s1277 commented ·
Issue is that the batteries are not at 13.5 even though it always thinks it is for some reason so they drain and dont charge?
0 Likes 0 ·
snoobler avatar image
snoobler answered ·

Nothing in the settings seems amiss.


You're referring to this?

1696715520898.png


1696715520898.png (273.7 KiB)
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

s1277 avatar image s1277 commented ·
yes
0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·

Is something else feeding the MPPT voltage, current or temperature data? Shunt?


Is it possible that the MPPT is below 41°F in the morning?


I'd try a "reset to defaults"1696729914656.png


reconfigure for LiFePO4 and then give it a another shot.

0 Likes 0 ·
1696729914656.png (78.7 KiB)
s1277 avatar image s1277 snoobler commented ·

Ill give the reset a try i do have a shunt and multiplus that monitor batteries but they show lower voltages than 13.5 more accurate I have the cerbo set to auto for selection of monitor . It has not been cold here yet so not below 41 I also have a dc-dc orion but engine isnt on


1696739131657.png

0 Likes 0 ·
1696739131657.png (28.8 KiB)
snoobler avatar image snoobler s1277 commented ·
Okay. Do you have DVCC on?


SVS, SCS and STS enabled?


How the heck can you have a battery indicating 10.04V and it showing 99%?

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·
I didnt see this but yes I do not know why it shows that
0 Likes 0 ·
JohnC avatar image
JohnC answered ·

@s1277

The evidence here suggests the mppt isn't actually connected to the battery.

The shunt shows 10.04V (Auto setting will choose the shunt), the Multi 10.21V, and you say the mppt reads 13.5V.

Check your wiring, fuse, etc.

Then hope you haven't actually damaged the battery by letting it get so low.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

s1277 avatar image
s1277 answered ·

I have the mppt connected to the batteries inline with shunt... it worked before


1696770277624.png

rvsolarwiringf.jpg


1696770277624.png (22.1 KiB)
rvsolarwiringf.jpg (1.1 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

Min voltage 8.05V?

Max voltage 14.11V?

126 hours since last full charge?


Do you have LFP batteries per the schematic?


If so, you have completely depleted them, and you are likely dealing with the BMS engaging in some sort of BMS protection. If there is an inverter in the circuit, when the BMS reconnects to the system, the surge from cap charging will typically trigger short circuit protection. The MPPT will then power the system in float since there is nothing to receive the charge. By resetting the MPPT, you're simply retriggering a bulk charge.


14.11V suggests that may not have ever truly fully charged the batteries.


Simply put, you are over-using your battery capacity and daily PV energy harvest. You need to fully charge them and stop depleting them. Set your equipment to stop using the batteries at 12V and avoid the BMS triggering protection.



16 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

s1277 avatar image s1277 commented ·

yes lfp. I have them plugged in on shore probablly be 3 days till charged weird they never would have been fully charged it was hooked up to 60 amp shore power for 45 days


yea I reset the mppt and whatever the absorb voltage is that is what it shows for the battery

I have a battery protect infront of my dc panel

thanks

1696803313887.png


0 Likes 0 ·
1696803313887.png (102.1 KiB)
snoobler avatar image snoobler s1277 commented ·

Most RV wiring is pretty crappy. Due to wiring losses, there is a significant voltage drop particularly at high current. What are your inverter charger settings?

Your connections are not ideal:

1696803757784.png


While some of this may be wiring losses, at a mere 13.3A charge current, you have a 0.28V drop. That's about 2%... that's really high for such a small current.


Recommend you confirm you configured your bank correctly, your main corrections are correct and all connections between battery interconnects are properly torqued.


I am convinced the MPPT issue is due to BMS protection issues. You're dealing with deeply discharged batteries, not an MPPT issue.


I don't see that you ever answered:

Do you have DVCC on?

If so, do you have SVS, SCS and STS enabled?


FWIW, your morning lows are below 41°F, so that could also be an issue. If the MPPT is not being fed separate temp data with STS, then I believe it may refuse to charge on mornings where the temperature is < 41°F when the MPPT turns on.



0 Likes 0 ·
1696803757784.png (101.0 KiB)
s1277 avatar image s1277 snoobler commented ·
it would not connect to my sisters starlink so I will have to get the info tomorrow or tuesday when I go check or if it connects to wifi overnight It does not like the starlink for some reason. I would say they are set to defaults if I had to guess Assume tey are all in the multiplus setting area


I will also verify nothing came loose on the lynx's or battery terminals


The batteries are inside the cabin under the couch in a battery box and have a heating pad for cold nights. I am in it in the winter so the cabin stays warm as well as the compartment with HW in it underneath. the cable runs are not long from the lynx to bateries. Last winter I didnt have issues, it would turn on every day get aground 500-600 from solar 400 some days. The issue started over summer I left the mouse deterrent on and it was infront of the battery protect (sincce moved it) and drained or it wasnt charging and the equipment Bluetooth and wifi depleted it.

0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·
Lots of folks use starlink without issue. I have it and am transitioning to it from DSL. When I was on site and testing it, Starlink seemed plenty reliable with VRM.


If you gain access again, you can download a VE Config file from the Device list menu, check/change settings and upload it.


The cable run from the batteries to the lynx don't matter a lot. It's the total run from the inverter/charger to the battery.



0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·
I will grab it today anything else that is helpful I use starlink as well on the road no issues think its her set up


the multiplus has a less than 2 foot run to the lynx distributor then shunt then lynx battery unit to batteries

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

Battery protect settings have remote plug pulled atm

img-3770.png

Solar after turning on that setting almost dark here


0 Likes 0 ·
img-3770.png (129.7 KiB)
img-3771.png (182.2 KiB)
s1277 avatar image s1277 snoobler commented ·

It is off and after 24 hours not looking good

img-3767.png


img-3766.jpeg


0 Likes 0 ·
img-3766.jpeg (1.4 MiB)
img-3767.png (348.8 KiB)
snoobler avatar image snoobler s1277 commented ·

Turn on DVCC and enable, SVS, SCS and STS (if a temp sensor is available).

If a temp sensor is not available, lower the cut off temperature to 34°F.

Also need inverter's charger tab on VEconfig. It shouldn't be sitting there at 13.2V doing nothing while on AC.


0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

Ok I did that made huge change on screen. The file u want I had to have my girl friend down load I am in Rv phone wouldn’t get file it’s on pc at home I will be here a bit is anything else is needed or remote access Solar still 0 but progress image.jpg

0 Likes 0 ·
image.jpg (1.6 MiB)
snoobler avatar image snoobler s1277 commented ·

If inverter was in storage mode, or float was set to 13.2V, you'd never get it charged on AC.

Recommend 14.4V absorption, 1 hour fixed duration

13.5V float. this will let the charge fall slightly from 100%, but not much, and it minimizes stress on the cells to maximize cycle life.


since you're limited to 14.5A AC input @ 120V, make sure PowerAssist is enabled. If the wiring can handle more than 14.5A, I'd push it to 75% of the circuit's maximum rating.


Try disabling and then enabling the MPPT in the battery settings screen to see if that will force start it and lower temperature protection to 34°F or disable altogether.

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

Where is power assist. It can handle more used it on 30 amp circuit

0 Likes 0 ·
img-3775.png (195.7 KiB)
snoobler avatar image snoobler s1277 commented ·
MPPT looks good. Confirm fixed absorption time of 1 hour in expert settings.


PowerAssist is on the Inverter tab in VEConfig


If all wiring and breakers can handle 30A, set AC input current limit to 24A.

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·
Can move to 24 amp. Thought I changed this to 14.5 when on a house breaker and 29.5 on a 30 amp one
0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·
Running a breaker at rated current will wear it out. I too will go to 14.5A on a 15A breaker just because that's already so low, but I like to respect the 75% rule on the higher rated breakers.
0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

Ezpert
img-3776.png

0 Likes 0 ·
img-3776.png (203.7 KiB)
s1277 avatar image s1277 snoobler commented ·

Just heard fan kick on on multiplus


0 Likes 0 ·
img-3769.png (514.5 KiB)
snoobler avatar image
snoobler answered ·

Are you telling me the BP is signalling the MPPT relay open? If so, why do you have the BP wired to a charging source?

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

s1277 avatar image s1277 commented ·
No BP is in front of dc output. I sent u that image thought u asked bout it the other day. I can look at the vrm and disable storage and upload it l8r. Was hoping it would come out of storage if I turned some stuff on but didn’t
0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·

I don't remember even thinking about the battery protect, so I got confused. In the MPPT settings you can toggle the charger:


1696890435175.png


This may trigger it to start charging by disable then enable.


Is it possible to share your VRM, so we can see what's happening?

0 Likes 0 ·
1696890435175.png (92.7 KiB)
s1277 avatar image s1277 snoobler commented ·
Sorry. I did toggle but it’s twilight here so tomorrow will tell more on solar
0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

it is not letting me upload the file or use it in my veconfigure 3

seems like my settings were lost for second ac out and bat type updated

we can do remote I finally got it on wifi

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

file on my onedrive https://1drv.ms/u/s!AolPyHW9OyCC913KkhgYCPARuckN?e=NYaUKQ


but cant get it to upload here

0 Likes 0 ·
s1277 avatar image
s1277 answered ·

I will make the updates but storage is off now also why does multiplus say 100% and how do i get rid of it

1696897424575.png


1696897424575.png (113.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

You've selected that battery monitor to be displayed in the GX. Once the Lynx shunt full charge criteria have been met, the Lynx will show 100%. Unfortunately, I have no experience with the Lynx shunt.


In Settings > System setup > Battery monitor - you should have the lynx specified.


In Settings > System > Battery Measurements - you can specify which battery monitors appear on the VRM dashboard. I personally like having them all displayed, so I can see what is going with multiple measurements.

19 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

s1277 avatar image s1277 commented ·
I just wasnt sure why multiplus shows 100%
0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·
Basically, because it's taken on more AC charge than it output AC. It can't see DC input from other sources or DC loads.


0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

so that is normal?

it shows 79.10A on multiplus this am

since it shows 100% will it keep charging to get to 800 amps?

1696944516195.png

0 Likes 0 ·
1696944516195.png (111.2 KiB)
snoobler avatar image snoobler s1277 commented ·

If PV or DC loads are part of a system, the inverter battery monitor will always be inaccurate unless it's being overridden by another battery monitor.


The Inverter will continue to charge while connected to AC until 14.2V is reached and held for 1 hour. It will then allow the voltage to fall to 13.5V where it will hold the battery at that level for as long as it's connected to AC power. It will also pass the AC power through to loads as well. If left on shore power, it will repeat the absorption charge and hold for one hour every 7 days.



I don't see the MPPT on the dashboard. Is it disconnected?

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·
it isnt realtime last update was a few hours ago in night so mppt wasnt on yet hoping it reconnects to wifi soon The connection at my sisters is terrible


so to get 800 amps it will take a really long time or never get there as configured?


also are there any other assistants or settings that would optimize

0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·

With 76A going into the battery per the monitor, that would take 800Ah/76A = 10.5 hours + the absorption time.


At 13.66V, you should be getting pretty close to full. The rise to 14.2V occurs very quickly at the end.


Given that the dashboard is from two hours ago, it might be finished by now. :)

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·
oh so thats the amounts it is charging at not the amps the battery has is there a way to see what the batteries are at or does that show once charging is complete
0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·

The lynx is programmed with the battery capacity. Once it achieves full charge, it will reset to 100% and should track relatively accurately provided the lynx is set properly.


due to the likely BMS cut-off, the Lynx lost power and is indicating "--" because it no longer knows the state of charge.


On the advanced tab you may be able to see the consumed Ah value change. You will have to look at how it's changed from the low to the high to calculate now much Ah has been input.


1696953245815.png


You can also estimate it from the average charge current on the graph multiplied by the number of hours it's been charging.

0 Likes 0 ·
1696953245815.png (76.7 KiB)
snoobler avatar image snoobler s1277 commented ·
Can you include your Lynx shunt settings?
0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·
as soon as it refreshes I will or when I go over there today
0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

See below shunt and so on

img-3781.png

img-3780.png

img-3779.png

img-3778.png

img-3777.png

0 Likes 0 ·
img-3777.png (362.4 KiB)
img-3778.png (282.1 KiB)
img-3779.png (330.8 KiB)
img-3780.png (374.3 KiB)
img-3781.png (384.5 KiB)
img-3785.png (151.9 KiB)
snoobler avatar image snoobler s1277 commented ·
Shunt is misconfigured. Recommend the following changes:


charged voltage 14.0

tail current 6%

peukert 1.05

Efficiency 98


Recommend you hit the Press to sync button. The battery is fully charged, but the charged criteria were not met.

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

Updated

img-3786.jpeg

0 Likes 0 ·
img-3786.jpeg (1.2 MiB)
img-3787.jpeg (1.0 MiB)
snoobler avatar image snoobler s1277 commented ·
the diagram shows this, but it's worth confirming, all devices connected to the battery must be connected on the non-battery side of the shunt.


Assuming the above is true, and provided the bank is fully charged a few times a month, % charge should track relatively reliably until power is lost again.


Were you able to confirm MPPT operation today?

0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

image-2023-10-10-204012130.png

screenshot-2023-10-10-203257.png

attached is a pic (not end state but lunx stuff didnt change so yes batteries then shunt then distribution


It never came on wifi today and was almost dark when I went over there didnt look like it did much in advanced stats


Was gonna ask should I unplug shore and let it run on just solar. I wont be back to it until sunday night or monday afternoon so I could do it then as well


I am assuming it will not be on wifi since it never does when I need it


whats best way to test




0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·

If someone is relying on the power, I would be inclined to keep it running as-is until you can get on site.

0 Likes 0 ·
Show more comments
s1277 avatar image
s1277 answered ·

Unplugged ac seem to always show same 22.4 v .2 amp from solar no matter if all or 1 of the panels connected. Going over there today to test with multimeter each panel and hook up my starlink so wifi stays on. How can I get you my vrm siter PW? dont want to put it here?

https://vrm.victronenergy.com/installation/269606/share/d3722b89


any thing else I should check?


1697380578524.png




1697380578524.png (111.6 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image snoobler commented ·

Today is daughter's birthday, so I haven't been paying attention.


You should be able to invite me without a password or share a direct link to your VRM.


0 Likes 0 ·
s1277 avatar image s1277 snoobler commented ·

they email ting didnt work for me

let me know when don so i can pw protect it

https://vrm.victronenergy.com/installation/269606/share/d3722b89

0 Likes 0 ·
snoobler avatar image snoobler s1277 commented ·

that's a read-only link, so no one can make any changes.


0 Likes 0 ·