Help! ESS discharge not reaching external control target

Hi there,

I'm using a Quattro 48/15000/200-2x100 with two BYD Premium LV batteries with ~31kWh of capacity. The Quattro is connected to the grid only (no other connections used).

With ESS in External Control and the system set to charge, the system does exactly what it is told to do (e.g. 5000 or 8000W).

If I tell it to discharge at a set rate (i.e., back-feed in to the grid), it works at small numbers (e.g., -1000W or -2000W etc) but if you put a bigger number in it never achieves it. As an example, with a target of -8000W set, the system seems to cap itself at approximately 2600-3000W or about 55-65A discharge from the batteries.

The BMS is reporting to my GX that the discharge limit is 432.0A, so that doesn't seem to be the issue...

Any ideas?

Thanks!

ESS
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

niborb avatar image niborb commented ·

Here are a couple of graphs to helpfully illustrate the issue...

Set to charge at 6000W (worked perfectly) and discharge at 8000W (nowhere near)...

Anyone got any ideas?

screenshot-2022-11-12-at-130654.pngscreenshot-2022-11-12-at-130725.png

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ niborb commented ·

@niborb

Grid resistance and voltage?

Derating?

0 Likes 0 ·
niborb avatar image niborb Alexandra ♦ commented ·
Grid voltage is well within tolerance though?


And we’re not actually exporting, this is just reducing our demand…

0 Likes 0 ·
niborb avatar image niborb commented ·

Has anyone got any ideas? Really struggling to get this 15kVA system to export more than 2 or 3kW! @Guy Stewart (Victron Community Manager)?

0 Likes 0 ·
shaneyake avatar image shaneyake niborb commented ·

What is the input current limit set to?
Can you confirm you are actually commanding -8000W?
What is generating the external control?

0 Likes 0 ·