Multiplus keeps reverting to passthru in ESS system

Hi

I have a 24V/3000VA Easysolar with a 150/70 regulator and a second 150/100 regulator with extra panels. 2 x UP2500 Pylontech batteries canbus connected to the Easysolar's color control.

The system works perfectly as an off grid system but I want to run it with a grid input under ESS. Every time I bring in the grid the system works fine for a few minutes then it starts to use the grid to make up any shortfall in the loads from the solar chargers. Then the grid takes over and the chargers reduce to zero watts when the battery gets full. instead of using the fully charged batteries it powers the loads from the grid.

ess.jpg

There is an ET112 smart meter installed as a grid meter.

Have been through all the things that might cause this in ESS FAQ 10.4 and 10.9.

1. GX device is seeing the meter

1698030486892.png

2. Canbus battery is connected

1698030567378.png

3. Discharge Limit is not stopping the battery from discharging

1698030687106.png

4. The battery is full and is set to stop discharging at 20% in ESS settings

5. Have tried Australian grid code and Other grid code and have tried turning off LOM settings on each to no avail.

6. I have checked the relay test is completed ok

1698030981351.png

If I restart the VE Bus system it runs normally for a few minutes then goes back to passthru.

Oh and the switch is in the on position not charger only.

All Victron equipment is at latest firmwares

Anything else I have missed?

I am a Victron Distributor and have installed dozens of these systems with very few problems.

Any help would be appreciated


ESS
ess.jpg (40.4 KiB)
1698030486892.png (24.6 KiB)
1698030567378.png (27.3 KiB)
1698030687106.png (20.7 KiB)
1698030981351.png (25.5 KiB)
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@Charlie D

Why is it showing 3 phases there when you have a single phase system?

0 Likes 0 ·
Hi @Charlie D,

Could you please posts a screenshot of the ESS settings summary from VEConfigure?

0 Likes 0 ·
charlie-d avatar image charlie-d Guy Stewart (Victron Community Manager) ♦♦ commented ·

Hi Guy


Here is the summary.

1698044686324.png

The system is on VRM

https://vrm.victronenergy.com/installation/302766/dashboard

Or do I have to give you some access to it

0 Likes 0 ·
1698044686324.png (55.8 KiB)
charlie-d avatar image charlie-d Guy Stewart (Victron Community Manager) ♦♦ commented ·
Hi Guy

Any thoughts on what is going on here, My client is getting a bit antsy about the constant grid use


0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ charlie-d commented ·

Hi @Charlie D,

Sorry I only just saw your reply, this is the ESS summary I was looking for, can you please take a screenshot of that?

This can be done remotely;

I am specifically looking to confirm all the voltage thresholds there are suitable for your battery - The defaults (as set in this screenshot) are not correct for Pylontech.

cleanshot-2023-10-30-at-113554.jpg

0 Likes 0 ·
charlie-d avatar image charlie-d Guy Stewart (Victron Community Manager) ♦♦ commented ·

Hi Guy


Sorry, here it is

ess-summary.jpg

Charlie

0 Likes 0 ·
ess-summary.jpg (51.9 KiB)
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ charlie-d commented ·
I've asked a colleague to have a closer look.
0 Likes 0 ·
3 Answers
daza avatar image
daza answered ·

Silly question, What is your battery setting on the Cerbo try changing it there ie keep battery charged, optimised and so on?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

danqcca avatar image
danqcca answered ·

Can you share a print screen of this zone ? : screenshot-20231031-234538-chrome.jpg

Mode, should be one of the 2 Optimized, try "without BatteryLife" at first.

Minimum SOC (unless grid fail) must be bellow 100%! In your case, from what i read, it is at 20% = perfect


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Charlie D


We've looked at your system remotely, I'll email you with some questions.


Edit by Guy Stewart - for others in the future who might be wondering, it appears to be an issue with his MultiPlus overheating - but nothing is confirmed as of yet.

2 |3000